Discuss RCD and bonding for pools/saunas in the UK Electrical Forum area at ElectriciansForums.net

Rockingit

-
Mentor
Esteemed
Arms
Supporter
Reaction score
6,409
Out on site and somehow all the books have walked out the van! Could someone do me a favour and look in the BGB and tell me if bonding is exempted if RCD is in place, and whether the RCD needs to be 2p or not? Not even sure what there may be to bond yet! Cheers muchly. R.
 
Swimming pools have no exemption from the supplementary bonding requirements. Protective measures of SELV or RCD or Separation(1 item). Should have an earth mat connected to supplementary bonding if PME supply.
Saunas have no exemption from the supplementary bonding requirements and all circuits in the location must be RCD protected.

RCD is as specified in 415.1.1 so no mention of double pole.
 
702.411.3.3 Additional protection: Supplementary equipotential bonding

All extraneous-conductive parts in Zones 0,1 & 2 shall be connected by supplementary protective bonding conductors to the protective bonding conductors of exposed-conductive-parts of equipment situated in these zones, in accordance with Reg 415.2

702.410.3.4 - Protective measures against electric shock ( Zones 0 & 1 )

ii) automatic disconnection of supply using an RCD having characteristics specified in 415.1.1

415.1.1 ...... not exceeding 30mA, operating time not exceeding 40ms at residual current 5In
 
Thanks chaps! Now have the major headache of trying to sort some bonding!!! May have to make do with a connection back to the DB earth (25/4 SWA) instead as the METs about 100m of serious building work away.
 
Thanks chaps! Now have the major headache of trying to sort some bonding!!! May have to make do with a connection back to the DB earth (25/4 SWA) instead as the METs about 100m of serious building work away.


If the supply at source is PME, the 25mm 4 core SWA installation is will not be sufficient as a bonding conductor!! You have a choice, run a separate bonding conductor back to the MET or install a TT system for the whole swimming pool installation. If TN-S your in luck, depending on the Zs values on a 100m of feeder/supply cable!! lol!!

What's the betting no-one provided a connection to the pools re-bar, or to link out from the re-bar to any metallic steps supports, or d/board supports?? lol!! That in it's own, would have given you more than a half decent Ra!!
 
If the supply at source is PME, the 25mm 4 core SWA installation is will not be sufficient as a bonding conductor!! You have a choice, run a separate bonding conductor back to the MET or install a TT system for the whole swimming pool installation. If TN-S your in luck, depending on the Zs values on a 100m of feeder/supply cable!! lol!!

What's the betting no-one provided a connection to the pools re-bar, or to link out from the re-bar to any metallic steps supports, or d/board supports?? lol!! That in it's own, would have given you more than a half decent Ra!!

It's not a pool, it's a 'pro' hot tub being installed at a holiday lets place so there is no re-bar etc etc. Once I'd had a good look around I actually decided that there probably won't be anything needing bonding in the building it's being installed in, and I'm guessing that the unit being installed is all class II and they'll use plastic pipe throughout. Which is just as well, really, as to put (as E54 correctly guessed) PME grade bonding in to that location correctly would just be a nightmare.

My plan is just to check in on Tuesday when the installers for it are there and look it over.
 
You may not be out of the woods yet!! lol!! Has the floor slab reinforcement been earthed/bonded, only ask because as the back of my mind somethings telling me that on PME supplied areas, where bare feet are going to be the norm (swimming pools/saunas/spar's etc) such buildings need a bonded floor grid!! I may be wrong Rockingit, so give it a quick check in the books ... lol!!
 
You may not be out of the woods yet!! lol!! Has the floor slab reinforcement been earthed/bonded, only ask because as the back of my mind somethings telling me that on PME supplied areas, where bare feet are going to be the norm (swimming pools/saunas/spar's etc) such buildings need a bonded floor grid!! I may be wrong Rockingit, so give it a quick check in the books ... lol!!

415.2.1 - Supplementary bonding shall include.....where practicable, the main metallic reinforced reinforcement of constructional reinforced concrete.

But nothing specific in section 702 that I can see. And thankfully I don't have the above situation to deal with! This is the floor of an old converted cider barn.
 
All i can remember off the top of my head, is that PME earthing can't be used in buildings used for housing livestock unless there is an embedded earthed floor grid. I believe there is/was something similar for indoor pool/spa installations or where wet bare feet is to be expected. As i say, i could be wrong here and confusing my self with something else. lol!!
 
Nothing in 17th that I can find that suggests that those same conditions for cows in parlours extends to swimming pools etc. Mind you - I've no knowledge of how ugly some of the users may be, so who knows?!
 

Reply to RCD and bonding for pools/saunas in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

So I know why it is done, where it is done and how it’s done, but I’m yet to see a scenario where there is shock danger in a typical bathroom in a...
Replies
31
Views
674
Hello. Non-electrician here. Failed an EICR yesterday as the electrician graded my consumer unit C2. Why C2 and not C3? He didn't say (and still...
Replies
22
Views
3K
Hi friendly people, As you may be aware, I'm a plumber, so quite possibly what I am seeing is correct, though it seems a bit odd to my untrained...
Replies
4
Views
5K
Hi guys, I've got a job where I'm installing dado trunking on the floor of an office for sockets and data. Some info on job - In total I will be...
Replies
18
Views
5K
Good evening all. I’m a new member and found this place by searching for some info on a problem that has developed. I used to be a sparky in the...
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock