Discuss Rcd and fuses in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Reaction score
1
Hi sorry a basic question.
I have no regs books and I’m still learning.

on a eicr would a board with no mcb e.g rewirable fuses be unsatisfactory c2/ or c3 or is it fine as long as it makes disconnection times.

also same with no rcd does this fail now as their most likely will be a circuit passing a bathroom or sockets that could be used outside.
 
rewireable fuses IMO would be a C3 if disconnection times were OK. could even be a C2.
as for RCD.. sockets for outdoor use, no RCD is a C2. other sockets usually a C3. bathrooms C3 if supplementary bonding is in place, otherwise a C2.
cables buried in walls< 2" deep, no RCD is a C3.
lighting circuits with no RCD is now a C3 under 18th Ed.

think that just about covers it.

the reason i may give rewiereable fuses a C2 is potential danger if a donut replaces fusewire with one of a higher rating. this is common, esp. with farmers who often use an offcut of barbed wire as a 30A fusewire.
 
Okay great thanks.
Just what did you mean by could be a c2 for non mcb.
Thanks
rewireable fuses IMO would be a C3 if disconnection times were OK. could even be a C2.
as for RCD.. sockets for outdoor use, no RCD is a C2. other sockets usually a C3. bathrooms C3 if supplementary bonding is in place, otherwise a C2.
cables buried in walls< 2" deep, no RCD is a C3.
lighting circuits with no RCD is now a C3 under 18th Ed.

think that just about covers it.

the reason i may give rewiereable fuses a C2 is potential danger if a donut replaces fusewire with one of a higher rating. this is common, esp. with farmers who often use an offcut of barbed wire as a 30A fusewire.
 
What do you think needs to be considered if at all with BS3036 fuses as this means of protection is still recognised by BS7671.
 

Reply to Rcd and fuses in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi everyone Sorry if it's a repeated question tho. Agents followed me a failed visual EICR which has C2 for lack of RCD on cooker circuit and...
Replies
11
Views
1K
I've recently has an EICR (report attached) carried out on my two bed flat because I need to rent it out for a year. The electrician has come back...
Replies
19
Views
985
Good Afternoon All Currently doing an EICR on common parts of a big site with multiple blocks. All blocks have outside garden spike lighting in...
Replies
11
Views
598
Good Evening. I’m currently carrying out an EICR. I have a cooker circuit radial with a 32amp mcb fed from and RCD split board. There is a 45amp...
Replies
14
Views
923
Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock