bathroomboy

Whats the best method to install new downlights and illuminated mirror and comply with the 17th, no rcd protection on the board, can upstairs lighting mcb be changed for a rcbo and run off this? or put in local rcd spur. Cheers
 
Yes, you can do either.

If you are fitting an RCD spur then its best to try and locate it in an airing cupboard rather then in the loft (if the room is upstairs).
 
Hey.

Personally would go for the RCBO, possibly less confusion in the event of fault - only having to go to one place for reset.

I would say it's worth doing a quick I/R test on the circuit involved first to identify any existing faults. If there are any you can advise the customer and if they dont want to shell out for repairs then you can always just go down the RCD spur route to protect the work you've done

Cheers:D
 
Thanks for the replies, this 17th is a pain as most of my work is in bathrooms, went to look at a job today, new bathroom suite etc in an old farmhouse, the room was originally a living room with chimney breast and alcoves, customer mentioned she would like an extractor fitting as well, there were sockets in room, at the db there were 3 phase for the farm outbuildings as well as the board for the house, I advised her to get a full time spark in, job was a nightmare, probably need a complete upgrade.
 

Reply to Rcd Bathroom lighting? in the Australia area at ElectriciansForums.net

Similar Threads

Evening everyone… I’ve attached pictures for your leisure.. so basically the customer does not have any RCD protection.. 3036 fuseboard is in...
Replies
9
Views
419
I put some news lights in a bathroom and new extractor fan. Did the tests and filled out form. A couple of days later another electrician came in...
Replies
2
Views
307
Hi folks. Need some help, wanting to add bathroom mirror with built in shaving port but don't want to chop into wall as I can't replace the tiles...
Replies
5
Views
2K
Good Afternoon All Currently doing an EICR on common parts of a big site with multiple blocks. All blocks have outside garden spike lighting in...
Replies
11
Views
587
Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock