I am not yet fully qualified and this is not a job I am going to take on so have passed it onto a qualified electrician , but out of interest I would like to understand it.
Domestic TT. CCU in house feeds (SWA) to a garage CCU (with an independent earth rod). Now someone has taken the feed from a ring main!! so looks like the earth in the SWA is not connected in the garage only in the house hence earth rod.
Both CCU's have 63A Rcd's, firstly If I remember rightly discrimination is not relevant on RCDs?
There was a fault (must be earth leakage) on a pump in the garage and the RCD in the house tripped but bypassed the one in the garage??
Obviously because this is connected to the ring it took out half the board in the house! I have heard of time delay s type RCD's, could this be used in the house?
What would you do?. I do intend to go down whilst the electrician is there and have a chat with him but also am scratching for some voluntary work with him so would be nice if I seemed a bit more clued up!!
Cheers chaps :stooge_curly:
Domestic TT. CCU in house feeds (SWA) to a garage CCU (with an independent earth rod). Now someone has taken the feed from a ring main!! so looks like the earth in the SWA is not connected in the garage only in the house hence earth rod.
Both CCU's have 63A Rcd's, firstly If I remember rightly discrimination is not relevant on RCDs?
There was a fault (must be earth leakage) on a pump in the garage and the RCD in the house tripped but bypassed the one in the garage??
Obviously because this is connected to the ring it took out half the board in the house! I have heard of time delay s type RCD's, could this be used in the house?
What would you do?. I do intend to go down whilst the electrician is there and have a chat with him but also am scratching for some voluntary work with him so would be nice if I seemed a bit more clued up!!
Cheers chaps :stooge_curly: