Discuss RCD not Resetting in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Reaction score
1
Hi there
Local church
TT system,
CU with RCD as protection as main switch.

Had a problem with the dishwasher tripping the RCD when running a intensive program, but that is a other issue.

the main issue is when the RCD has tripped, you cannot reset it.

There usually is no power on the circuits, as the church has been empty when the RCD tripped, maybe fridge, dishwasher, boiler etc, no lights or PA system etc.

I have traced the fault back to the two computer suites they have, one in an office, one in the main hall, both on seperate circuits.
I understand that this may be a high integrity problem and earth leakage in both these systems.
What I dont understand is why just turning off the MCB's those two circuits does not allow me to reset the RCD, but turning off all the MCB's does let me reset the RCD.

I have disconected the computer equipment from the circuits and am able to reset the RCD with all MCB's on so it's nothing else causing it.

any ideas or answers as to why this happens.
 
have you done a ramp test? have you tried measuring leakage?
 
No I havent mainly because the computer suites do not trip the RCD, We suspect the dishwasher is tripping the RCD.

As a test.

I disconnect the Dishwasher and manually trip the RCD, at this point I cannot reset it until all the MCB's are turned off.

the question is why do I have to turn ALL the MCB's off before I can reset the RCD.
 
i've had this with some RCDs. had to turn off all breakers, reset RCD , then turn breakers back on.
 
I have tried another make of RCD
80A 30ma

As per Telectrix's post
just wondering why this is the case.

physically disconnecting the computer items from the circuits ie unplugging them causes the RCD to reset normally with all MCB's on.
Plugging in the Computer stuff, but not turning on the computer stuff DOES NOT trip the RCD, but when the RCD is tripped and the computer stuff is plugged in but turned off, the RCD will not reset unless all MCB's are turned off.

I cannot see how an IR test will do anything, nor ramp testing etc the RCD, because as far as I can see there is no fault with any of the circuits, just a problem caused by the earth leakage of the computer stuff, but why does it seem to affect all the MCB's
 
I don't do domestic stuff I work in industrial settings but to me its pointing to the cpu's and I think (pretty sure) that in a CPU line and neutral both connect to earth through filters (capacitors) perhaps the fault lies there?

How old are the computers?
 
I thing we’re looking at a cumulative leakage problem. If the circuits are turned on individually the build up is gradual and not pushing the RCD over it’s trip limit. As with all protective devices an inrush will cause tripping. Being in the industrial sector you should know this.
As to curing the problem. The loads need splitting across a couple of RCD’s. And sort the dishwasher out.
 
I have tried another make of RCD
80A 30ma

As per Telectrix's post
just wondering why this is the case.

physically disconnecting the computer items from the circuits ie unplugging them causes the RCD to reset normally with all MCB's on.
Plugging in the Computer stuff, but not turning on the computer stuff DOES NOT trip the RCD, but when the RCD is tripped and the computer stuff is plugged in but turned off, the RCD will not reset unless all MCB's are turned off.

I cannot see how an IR test will do anything, nor ramp testing etc the RCD, because as far as I can see there is no fault with any of the circuits, just a problem caused by the earth leakage of the computer stuff, but why does it seem to affect all the MCB's

computers are always drawing power. the 5v rail inside is always on. this could be why its tripping it.


this is because most pc psu are cheap crap
 
i heard that in college.

cant put more than 5 pc's on one radial circuit due to a lot of earth leakage as a result. ( just what ive heard, not that ive ever installed in a computer room)

???
 
Yes i understand all that, but still I don't understand why I have to turn off all the MCB's in order to Reset the RCD!!!

You say they are turned off , but is it a 2 pole switch in the socket outlet ?
Why don't you just ramp it and find where the underlying fault / faults is , because it sounds like Tony is spot with his thoughts on .
 

Reply to RCD not Resetting in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi I am asking for help as a novice and 1st time user of this forum. Recently started to experience tripping of MCB & sometimes with the RCD at...
Replies
7
Views
554
Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
343
Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K
Hi, I have lifetime experience (50+ years) in United States with basic knowledge of split phase 120/240 volts replacing wall switches and...
Replies
5
Views
498
My circuit panel has two banks of breakers, each bank protected by an RCD. One of these RCDs has been problematic in that it trips intermitantly...
Replies
12
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock