Discuss rcd not tripping on test in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
110
Hi All
Changed a C.U today, Volex (not my choice but customer supplied it) Dual RCD, one 80A & one 63a. All test results good except on RCD test at socket outlets. on half test all OK, on 5 x test all OK but on 1 X test @ 180 no trip but fine @ 0. Ramp test ok. When tested at RCD with mcb's open they both test out OK. Any ideas please.
 
you should test the RCDs at the RCDs , with no loads applied. if they test OK< then fine.
 
I tested at RCD's with all breakers off and were OK, but why when tested at sockets did they not operate at 1 x and only one 1 side of the cycle, all loads were disconnected
 
I would point it out to the client and note it on the cert.

If we supply the unit we would replace faulty items under warranty at no cost to the client.
If the client supplies parts then I charge for labour only and they take the hit on labour if something is faulty
 
I would point it out to the client and note it on the cert.

If we supply the unit we would replace faulty items under warranty at no cost to the client.
If the client supplies parts then I charge for labour only and they take the hit on labour if something is faulty
Good point. If the customer supplied and insists on the parts that is not down to you. Are the RCDs branded or no-name types?
 
Brand new Volex 10 way dual RCD unit out of the box, do you think faulty RCD's and if so why do they work OK when tested at the RCD but not when tested further along the circuit.
 
Brand new Volex 10 way dual RCD unit out of the box, do you think faulty RCD's and if so why do they work OK when tested at the RCD but not when tested further along the circuit.
Was just a thought. Are thereany inductive loads on the circuit which could influence the test? Strip lights, soft starters, filters etc?
 
This is from a non domestic experience: RCD tests failed, I suspected a faulty cable, it went up through a false ceiling, then it was spiraled round the sprinkler pipe (!). Once I re-routed the cable the tests were OK.
 

Reply to rcd not tripping on test in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
320
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
789
I'm writing this mainly hoping something occurs to me while writing it! I got called to an occasionally tripping RCD. It's a Hager double height...
Replies
19
Views
2K
Cant get my head round this :( I understand N-E faults cause RCD's to trip, but I cant understand why on these 2 occasions, googled allover but...
Replies
13
Views
1K
I just finished a garden room supply. The customer already had a CPN garage consumer unit that the last sparks left there, brand new in box, and...
Replies
2
Views
879

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock