Just been called out to install cooker circuit. 6mm and 45A Isolator Switch, obviously dedicated circuit. Existing Wylex D/B with 1 Ring for whole house on RCBO, 2 Lighting not RCD. 1 Spare way with 16A MCB, assume was for Immersion Heater, no longer used. Changed 16A MCB for 32A and connected cooker cable to this. My query is ___ should I put RCBO instead as the new circuit is all surface, no buried cables, only a 3m run in cupboard under stairs, thtough studded wall into kitchen surface clipped under kitchen unit to Isolator, then to Connection Unit behind cooker. The problem with fitting RCBO is that it won't fit as the neutral bar is just above the MCBs and would stop the RCBO fitting on the DIN Rail. I have adviseed the client that the D/B should be upgraded.
 
Assuming there is no socket outlet on the isolation switch,and u can verify no buried cables,(that is all cables in trunking etc),then u are half way there..however the disconnection time on that circuit still has to be met without the rcd,..and if its a tt system it wont be!
 
that's what i thought. i get R1+R2 of 0.02 and Zs reading of 0.30. seems ok to me.
 

Reply to RCD or Not in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

I'm obviously still new and learning about what I can and cannot do, but essentially I want to install an EVSE at my own house for an electric...
Replies
8
Views
603
We have a room in the house that was the kitchen. That has been relocated to a different area, so the old kitchen has been sold off and the room...
Replies
2
Views
676
Doing a kitchen job for my daughter’s music teacher, who also happens to have been in my wife’s class at school. Nothing big… just a little...
Replies
2
Views
298
Hi all, I'm about to replace our kitchen and one of the upgrades is to install two full size ovens to replace the original twin over under...
Replies
7
Views
1K
Cooker circuit has B40 MCB in the CU for the cooker, confirmed wired to the cooker outlet throughout, via a cooker switch & socket with a 10mm...
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock