Discuss rcd protection- barber shop in the UK Electrical Forum area at ElectriciansForums.net

J.C.E

-
Arms
Reaction score
158
afternoon guys

think i know answer to my question but wanted to double check

my barber (quite friendly with him so wanted to help him out!) asked me to do his barber shop eicr (only a small 6way c/u) anyways just had a brief look and its an old board with wylex push in reto 60898s- no rcd protection

the shop is ground level

would you guys c2 no rcd protection to socket outlets or with commerical is it different?

head says it just same as it would be for domestic so c2
 
On site guide. 3.6.2.

Omission of RCD Protection

In the following circumstances.

Non domestic premises, where a documented risk assessment determines that RCD Protection is not necessary.
 
If a non rcd protected socket was right by an external door and likely to be used for outdoor equipment C2, otherwise C3 for the ground floor sockets. (Providing acceptable EFLI readings obtained)
 
@buzz I believe the above document is irrelevant, the op is asking about an EICR not a new install.

Also the document is not current, its pre amendment 3.
 
I'm not sure what point you're trying to make here? You stated above you'd C2 sockets without RCD protection, which in general is incorrect for domestic or non-domestic.
 
Are they likely to be using Portable /mobile equipment outside?
Do any unprotected sockets give rise to danger?(external influences)
This would influence my choice of code
 
Last edited:
Tis not the socket which gives rise to danger but appliances using said sockets. Don't worry about the ifs and maybes the fact is they have no rcd protection and this is the statement of fact you use, Code it, move on.
 

Reply to rcd protection- barber shop in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello! I've been racking my brain this evening about some RCD selections. I've been doing some work for a solar installer, and they've asked me...
Replies
5
Views
931
Good Afternoon All Currently doing an EICR on common parts of a big site with multiple blocks. All blocks have outside garden spike lighting in...
Replies
11
Views
539
Hi all, Just a quick one regarding the need for RCD protection for socket outlets rated up to and including 32A. I have been tasked to install...
Replies
17
Views
2K
I'm doing a college design project and need to choose a suitable range of circuit protective devices for the whole contact. I've chosen and...
Replies
7
Views
3K
Good day. First time poster. We recently had an electrician perform the EICR, as this is a newly purchased property I thought'd I would have the...
Replies
7
Views
720

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock