Discuss RCD Random Tripping in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
116
Evening all. Just after a bit of advice. Just been out on a job where they have had Random tripping of one of the RCD's on a split load board. They were told by a previous electrician it was the shower so that got replaced, problem continued. Another electrician said they had a cracked shower pull cord box and damp was getting in so he replaced that. Another replaced the RCD and the saga continues and I got called in.

Last night, mulling over my options with the info I had I though it sounds like a N-E fault so i'll megga all circuits and see what I get. Anyway all about what you'd expect for the age, although ring circuit was down to 40MΩ. Oven circuit >999MΩ N-E however with the oven back in circuit 7MΩ N-E. Although not a fail would you say this would be low enough to give intermittent trips of an RCD when under load. Funnily enough they could not replicate the problem tonight but they are convinced it has happened when they have had the oven on. Also to note when I removed the front plate of the 45A oven switch the line feed fell out and was not screwed down at all, could this have caused the RCD trip?

Any tips would be appreciated, i'm back there saturday...

Also to note RCD tests are fine and ramp test no apparent issue with the RCD and in any case has been replaced.
 
7 Meg ohm will not trip an rcd however there maybe a fault with the oven which only occurs when it is operating. A loose connection can cause an rcd to trip so maybe you have hopefully resolved the problem. Don't take for granted it is the oven just because the householder is convinced it is the cause.
 
Fridges or freezers are always worth a look. Try plugging it into a socket on the other rcd for a few days and see if the tripping then affects that rcd. These intermittent faults are always a pain.
 
Hi,
You DO need an earth leakage tester to fault find this, any appliance with an earth connection may legally leak up to 3.5mA through the mains filters and you will not see this on a megger test. A 30mA rcd must trip between 15mA and 30mA.
 
Hi,
Have a read www.beama.org.uk/asset/7EE14AAB-81DB-4870-A9ACFBC5C58A94A2/
Thanks mate, i'll have a read, looks very in depth but should be a useful bit of reading.

Anyway, not wanting to spend an arm and a leg on one, I watched a review and video on youtube and have ordered one of these:
Just shy of £80 with next day delivery. I'm back at the customers Saturday so i'll post back here how I get on.
 
I have had this before. It will definitelybe an appliance but which one is the question.
Ovens when they heat up is a common one, tumble dryer and washing machines half way through their cycle again is a common one.
How I do it is
Put a long cable from the CU MET to a stand alone met
Move all bonding to that met
Clamp the long length of cable
stick several appliances in at the same time
Wait till you get some current on the Clamp (only a few ma) then start dropping circuits till you identify the circuit
Then break that circuit down (appliances) till you find the offending item
 
Bit
I have had this before. It will definitelybe an appliance but which one is the question.
Ovens when they heat up is a common one, tumble dryer and washing machines half way through their cycle again is a common one.
How I do it is
Put a long cable from the CU MET to a stand alone met
Move all bonding to that met
Clamp the long length of cable
stick several appliances in at the same time
Wait till you get some current on the Clamp (only a few ma) then start dropping circuits till you identify the circuit
Then break that circuit down (appliances) till you find the offending item
Bit lost, what is the long length of Cable?
 
I have had this before. It will definitelybe an appliance but which one is the question.
Ovens when they heat up is a common one, tumble dryer and washing machines half way through their cycle again is a common one.
How I do it is
Put a long cable from the CU MET to a stand alone met
Move all bonding to that met
Clamp the long length of cable
stick several appliances in at the same time
Wait till you get some current on the Clamp (only a few ma) then start dropping circuits till you identify the circuit
Then break that circuit down (appliances) till you find the offending item

Usually easier to just clamp around both tails together. After all, it's the differential current in the supply that an RCD is actually detecting.
 
Hi,
You DO need an earth leakage tester to fault find this, any appliance with an earth connection may legally leak up to 3.5mA through the mains filters and you will not see this on a megger test. A 30mA rcd must trip between 15mA and 30mA.

Been in the trade nearly 40 years, fault find RCD tripping issues every week. I don't own an earth leakage meter and am not planning to buy one. Useful yes....essential no.
 
Massive pain in the ****. I've just been back to an intermittent fault on a new build. In the end, the ramp test on the rcd was low but not out of the spectrum just very very low. I replaced and the nuisance has gone.
I'd guess there's a fault on an appliance rather than any actual circuit. 1meg and under is a fault(it used to be 0.5meg by the way). If your getting 7meg that's a good reading.
Anything over 50megs fantastic.
There's been a lot of rain again, is it something external, only causing an issue when it rains.
Good luck.
 
Massive pain in the ****. I've just been back to an intermittent fault on a new build. In the end, the ramp test on the rcd was low but not out of the spectrum just very very low. I replaced and the nuisance has gone.
I'd guess there's a fault on an appliance rather than any actual circuit. 1meg and under is a fault(it used to be 0.5meg by the way). If your getting 7meg that's a good reading.
Anything over 50megs fantastic.
There's been a lot of rain again, is it something external, only causing an issue when it rains.
Good luck.
 

Reply to RCD Random Tripping in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Cant get my head round this :( I understand N-E faults cause RCD's to trip, but I cant understand why on these 2 occasions, googled allover but...
Replies
13
Views
1K
I'm writing this mainly hoping something occurs to me while writing it! I got called to an occasionally tripping RCD. It's a Hager double height...
Replies
19
Views
2K
Hi, Just been scratching my head about this one and wonder if I've missed anything. A few weeks ago I installed a new circuit for a 3kw oven and...
Replies
6
Views
799
Hi Guys, I'm having trouble diagnosing a fault on a customers downstairs socket ring, which only ever trips when the washing machine is used. The...
Replies
22
Views
3K
My circuit panel has two banks of breakers, each bank protected by an RCD. One of these RCDs has been problematic in that it trips intermitantly...
Replies
12
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock