Client is having some refurbishment in an office and i am tasked with relocating/removing/adding some sockets due to walls being moved etc.

Currently none of the sockets in the building are protected by any RCD/RCBO. The majority of the cables feeding sockets will be t&e ran under floor grates to floor boxes of 4x twin sockets. Some however will be chased into solid walls. My initial thought was to cover ourselves the best course of action would be to put all circuits feeding sockets onto and RCBO back at the board, however alot of the sockets will have computers plugged into them and this can create induced DC voltages causing the Rcbos to trip which would have a potential to affect the clients work. I am also unaware if they will have a competent i.e maintenance employee who has a knowledge of RCD/RCBOs on site?

Finally with the possibility of any ground floor sockets being used to supply any equipment that may be used outside (highly unlikely but never the less) should then all ground floor sockets be protected by an RCBO? Any advice appreciated.
 
I think you can leave them on mcb if a risk assessment explains why.

Any cables buried in wall should be protected.

mark the sockets as computer use only. This dissuades anyone plugging in the wrong equipment that could be used outside and covers your behind.

have another rcd protected circuit dedicated for outside use, or cleaners equipment etc.
 
10 x double sockets per rcbo.
gives 3ma per twin socket of leakage before tripping.

more than that an you CAN get nuisance tripping with computers, screens, photocopiers, printers.
they all have a little earth leakage and what i have found is especially if the supply is a little "noisy" random tripping can occur when the psu's dump the electrical noise.
 
Most RCBO are type A RCD part so are fine with typical PC faults. As above, you typically see 1-3mA leakage per PC so limiting them to a 10 or so per RCBO is one approach.

If it were servers in a rack (with additional grounding) I would be inclined to keep it on MCBs with appropriate warnings, but if office PCs and other stuff plugged in then definitely RCBOs, just split the circuits in to manageable chunks. Personally I am a fan of the RFC and here the added high-integrity earthing is useful as you are looking at high leakage currents.

As for ground sockets (and sockets in general) then yes, put them on RCBOs as well.
 
A documented risk assessment must be carried out by the client outlining the reason/s for omitting additional rcd protection this is then attached to the certification. This is the only stated way in BS7671 to omit additional protection. Of course you can fit warning notices to the sockets however this alone will not satisfy BS7671.
 
I have held my tongue long enough to many on here tend to think the fist stage is a "Risk Assessment", before a "Risk Assessment" is carried out a "Hazard Analysis" must be prepared, if that "Hazard Analysis" indicates that the "Risk" is minimal then further investigation is not required, if however the "Hazard Analysis" indicates that a "Hazard" is present then a "Risk Assessment" is carried out and a "Method Statement" is prepared of how that Risk is to be managed the "Risk Assessment" is not a control document.
 
A "Risk Assessment" is just that it list the risks possible from the "Hazard Analysis" it does not list the control methods as you say, but, if the control methods are not listed in a "Method Statement" the process has not been completed and would be found wanting in Court, been there done that.

Illustrate what you would do after carrying out a "Risk Assessment"?
 
Risk assessment, hazard analysis, method statement...

*sits back and waits for the outcome*

Its as big an argument as trump / biden...... or even ring / radial!
 
1. Hazard is present, additional rcd protection not being provided.
2. Risk assessment, clients problem.
3. Method statement, clients problem.
 
Not withstanding if you think it is not your problem, it was the process that I was questioning, most on here seem to go straight into the "Risk Assessment" without any consideration for the required "Hazard Analysis" when the structure of the process is clearly indicated in HSE guidance.
 
Not withstanding if you think it is not your problem, it was the process that I was questioning, most on here seem to go straight into the "Risk Assessment" without any consideration for the required "Hazard Analysis" when the structure of the process is clearly indicated in HSE guidance.
What has this to do with the OPs query. BS7671 asks for a documented risk assessment which the client carries out.
 
Nothing, it was an observation on the incorrect use of "Risk Assessment" prior to a "Hazard Analysis" being carried out, as I said earlier a "Risk Assessment" by itself is useless, without its correctly documented procedure and being taken to its conclusion with a "Method Statement" if required by the contractor carrying out the work, not the client!
 
Last edited:
What has this to do with the OPs query. BS7671 asks for a documented risk assessment which the client carries out.
Just thought I would clarify the above: If the installation is on a commercial premises then indeed the Principle Contractor or Principle Designer may well prepare the "Risk Assessment" and then ask each contractor for their "Method Statements" if however the premises are domestic and you as the contractor are the only contractor on site then you are the Principle Contractor and Principle Designer and the process falls to you and not the client. (CDM Regulation 7)
 
Just thought I would clarify the above: If the installation is on a commercial premises then indeed the Principle Contractor or Principle Designer may well prepare the "Risk Assessment" and then ask each contractor for their "Method Statements" if however the premises are domestic and you as the contractor are the only contractor on site then you are the Principle Contractor and Principle Designer and the process falls to you and not the client. (CDM Regulation 7)
Nothing needed clarifying. It is commercial the risk assessment is for omitting additional rcd protection carried out by the client. The RAMs required from the OP is for their working methods which are a separate issue.
 

Reply to RCD/RCBO in an office refurbishment in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

hi all come across a new build commercial office where radial circuits feeding electrak power track was protected by 32A RCBO at dist board and...
Replies
15
Views
1K
We have a customer in a large office block with all power in the building fed from an Electrak plug in busbar system. Lots of desks, lots of...
Replies
7
Views
547
Hi all Now being upfront I am not a sparks. I am about to have some work done by a friend (certified) and as he is doing me a favour I want to as...
Replies
5
Views
1K
So here is the thing Rhere is an old MEMSHIELD TPN+E Board that is pretty mich obsolete. The only place that sells their breakers would be Ebay...
Replies
5
Views
804
Hello, I have a hypothetical question (I'm an electrical engineer) to better understand RCBOs and how they are used in the USA. Let's say I would...
Replies
9
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock