R

radiohead

Testing 2 RCD's in a starbreaker dual board today. MCB's off and testing to the busbar both RCD's @5x, both RCD's gave exactly 4.8ms. Far too quick...and to get the same result on both RCD's didn't seem right. So I tested at two different sockets, both RCD's gave 4.8ms again despite connected loads including a fridge compressor running which would normally dramatically increase the recorded trip time. Suspecting a meter malfunction (ETHOS 8400...dont buy one!) I went back to the office and tried it on our RCD socket which we use to check the meters consistency, 18.6ms bang on the usual reading....so why did the crabtree units produce such clearly inaccurate readings?
Any suggestions?
 
Any chance of getting the starbreakers tested with another MFT? Or even the office ones tested on another MFT to see if the 18.6ms is trustworthy as well.
 

Reply to RCD test oddity in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
839
Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
2K
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
886
I did a board change this week and fitted a BG dual RCD. Carried out all my testing before hand and everything checked out ok. Fitted the board...
Replies
12
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock