Is there anyway I can test an installation without an RCD so I can be sure when I changethe board the RCD will trip in time? Or calculation, such as V/R eg 230/Zs.????
 
^^what he said, about what they said ^^
wonder if the OP will return...

About as much chance as Gary Glitter making one to the charts
 
Is there anyway I can test an installation without an RCD so I can be sure when I changethe board the RCD will trip in time? Or calculation, such as V/R eg 230/Zs.????
Try to have a good hard think about that one Jonesy. Then come back to us mate
 
Since the maximum Zs required for a 30mA RCD to trip is 1667Ω as this meets the RA x Idn <= 50 V, you can ensure that the disconnection times will be met before installing an RCD.
Being able to test the RCD to ensure correct operation by disconnection within 40ms at 5 x Idn is not possible without the RCD.
 
Is there anyway I can test an installation without an RCD so I can be sure when I changethe board the RCD will trip in time? Or calculation, such as V/R eg 230/Zs.????


Normally the questions around RCD's are


If I change the fuseboard how can I be sure the RCD will hold etc etc so this is a new one!


Looking at the ops previous posts he is working as a electrician so I hope this is just a blonde momment question!
 
Nine times out of ten trev!
When the RCD hasn't been installed?
An IR test is usually performed with the cables in question disconnected, please explain how a result of, for arguments sake, 100 Megohms between line and neutral will tell you if an RCD will trip in the event of a fault occuring on that circuit at an unspecified point in time in the future.
 

Reply to RCD test without RCD in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
343
Hi, I seem to have an RCD that keeps cutting the power at random times without actually tripping, if I reset it, the power comes on and will stay...
Replies
7
Views
478
Cant get my head round this :( I understand N-E faults cause RCD's to trip, but I cant understand why on these 2 occasions, googled allover but...
Replies
13
Views
1K
Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
Replies
6
Views
1K
Hi I am asking for help as a novice and 1st time user of this forum. Recently started to experience tripping of MCB & sometimes with the RCD at...
Replies
7
Views
556

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock