Discuss rcd tripping during the night and insulation resistance testing question in the UK Electrical Forum area at ElectriciansForums.net

There's no need to link L-N to IR test to earth for fault finding. The linked L-N method of IR testing is for initial verification of a new/altered circuit, or periodic testing. Fault finding does not follow standard test procedures as required for the above, if you link L-N you will not know whether the fault is L-E or N-E

He is testing with loads connected so L&N are connected across the loads.
 
What a lot of confusingness.

1. Testing IR to find a leakage fault does not require L-N test, which in any case you should not do (and cannot get a meaningful result from) when loads are connected.

2. When testing to earth, the loads will usually link L & N together by a low resistance so the readings of L-E and N-E tests will be the same. Therefore, there is no point doing these two tests separately with loads connected.

3. Just in case the only parts of loads connected between L & N are not of low resistance and cannot stand 500V without damage, you should solidly connect L & N to prevent that any voltage appearing between them. Therefore, only one test can usefully and safely be done, which is from L & N linked, to E. This is how a PAT tester tests insulation.

4. Most devices can withstand 500V on this test, or put another way, if they can't they aren't truly safe. But any appliances or cables with surge protection will give a failure reading, usually something under one megohm, as the surge protection clamps the 500V test voltage. They will usually pass easily at 250V, so that is a good reason to use this voltage when doing a global test to localise a bad load device.

5. Tracing a fault on the installation itself, with all loads disconnected, can and should be done L-E and N-E separately at 500V.

Not all leakage is due to poor IR but it is a good place to start.
 
If your IR tests are showing good then don't rule out a faulty RCD and/or a loose connection somewhere arcing.This seems to trip RCD's as well but don't know why.Also don't rule out damp and slugs which can come and go which is great fun when your testing the following day with no faults showing:(
 

Reply to rcd tripping during the night and insulation resistance testing question in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello all, I hope you're all keeping well. I have a question regarding insulation resistance testing. Whether doing a single circuit IR test or...
Replies
9
Views
637
Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
374
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
848
I sorted the fault fairly quickly as it happens but only because I'd come across it once before and at the time a few people said it couldn't...
Replies
13
Views
311
Commissioning a busduct. My contractor has installed a 2000amp aluminum Busduct in a 17 floor office tower. The specifications state you should...
Replies
0
Views
529

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock