S

sparkyork

hi all, first of all ive just got in from work, had they day from hell and im shattered! did a consumer unit change, test and a couple of minors works all on same job, as well as having to repair a pipe that was not supposed to be wear i was clipping (fecking plumbers!) they never heard of zones!

anyway all was well new board running nicely for a few hours, i did get a low ish reading on N-E on upstairs lighting of about 8 Mohms, but didnt think it would cause rcd to be a prob as ive always had much lower readings on rcd faults due to insulation resistance.

rcd only trips when the landing ceiling rose is switched ( i think ), there was an old energy saving lamp in it that i noticed was just flickering which seemed odd, like it was backfeeding off something?? any way took the bulb out reset rcd and tried the switch again, "trip" off it goes, disconnect lampholder just leaving rose and i can operate switches and its ok (so presuming strappers have gotta be ok, as i tested these when Ins Testing anyway)

didnt have a spare lampholder in van so couldnt try a new one, im off back there tomorrow afternoon, anyone got any ideas for a tired fellow spark!?

ps both rcd's are going, which also dont seem to be a compliance with the 17th either!!! sure it sounds like some sort of strappers problem occuring when a load is been switched but im confised.com
 
Last edited:
sounds like borrowed neutral problem upstairs lights have upstairs neutral. And i'll guess the feed is taken from the 2g 2way on the downstairs circuit.

Mark
 
cheers mark i was thinking on the same lines me self spesh as its all ok at the minute but as soon as any load is applied to that rose it all goes. why did they have to wire it like this!!

but why would it do it with a lampholder wired in and not trip when it was out?? the lampholder wiring is above 500M ohms
 
Last edited:
Just to give you something to do in the morning and keep you outta the pub

Mark

cheers mark i was thinking on the same lines me self spesh as its all ok at the minute but as soon as any load is applied to that rose it all goes. why did they have to wire it like this!!

but why would it do it with a lampholder wired in and not trip when it was out?? the lampholder wiring is above 500M ohms

Sparky its tripping out because 1x lighting circuit is connected to both RCDs

You need to take a neutral to the landing light from the downstairs circuit and take out the neutral that is there now

,Mark
 
Last edited by a moderator:
yeah now ive had chance to relax it all makes sense now!! im gonna have to reconnect the upstairs neautrals tho cos there looping off to something esle as well.
 
cheers mark i was thinking on the same lines me self spesh as its all ok at the minute but as soon as any load is applied to that rose it all goes. why did they have to wire it like this!!

but why would it do it with a lampholder wired in and not trip when it was out?? the lampholder wiring is above 500M ohms

I understand the borrowed neutral thing ,but cant get my head around why it trips with the lamp removed,:confused:
 
Rum it doesnt trip with the lamp removed (unless I've had one beer to many) no load.

what hes saying is with the lamp holder connected it trips and disconnected it doesnt .i presume that he removed the lamp first ,still cant get my head around it maybee i need another beer :)

cheers mark i was thinking on the same lines me self spesh as its all ok at the minute but as soon as any load is applied to that rose it all goes. why did they have to wire it like this!!

but why would it do it with a lampholder wired in and not trip when it was out?? the lampholder wiring is above 500M ohms

~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
####################################################
####################################################
'''''''''''''''''''''''''''''''''''''''''''''''''''''''''''''''''''''''''''''''''''''''''''''''''''''''''''''''''''''''''''''''''''''''''''''''''''''''''''''''''''''''''''''''
@@@@@@@@@@@@@@@@@@@@@@@@@@@@@@@@@@@@@@@@@:eek:
 
Last edited by a moderator:
ill confirm this wierd occurance tomorrow and post here!!

with an energy saving bulb fitted it was flickering slightyl and trippiing both rcds when switch was switched. i took bulb out and its still did it!! disconnected lampholder and everythings ok. i really dont get it either but thats how ive been able to leave the house tongiht so they can have some lights on!!

i will check again tommorrow, i even wondered of maybe the screws holding the rose up might be nicking the neutral above or something, but like easy and everyone else says as well as logic, it should only do it under load?????
 

Reply to rcd tripping on landing light!! in the Electricians' Talk area at ElectriciansForums.net

Similar Threads

Suggestions / solutions please anyone? I have a 2 way switch, Hall and Landing, power being fed on Landing. When the switch is turned on, the...
Replies
2
Views
542
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
850
An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
Replies
4
Views
1K
Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
374
Hi, I swapped a 2 gang switched socket for a 2 gang switchless socket with usb ports downstairs. I switched off all the power to the house by...
Replies
8
Views
808

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock