Discuss RCD tripping, problems identifying fault in the UK Electrical Forum area at ElectriciansForums.net

leep82

-
Arms
Reaction score
131
I received a phone call from a friend the other night telling me his socket werent working and whenever he tried to reset the MCB the RCD would trip immediately. As i couldn't get to him that night i asked him to unplug anything in the affected sockets and then try to reset the MCB, hoping that it may have been a faulty appliance. It wasnt!

I managed to get round to him the next day and repeated the procedure myself for piece of mind only to get the same results. I asked my friend if he had been doing any work around the house just before he noticed the MCB had tripped, which he told me he hadnt, although he had attempted to change a halogen lamp in his kitchen.

The board is a split load type with 100ma time delay RCD protecting two lighting circuits and a 30ma RCD protecting all other circuits. I started to test the circuit and although when doing my insulation resistance test L-N was low. I didnt think it low enough to create a short ( think it was over 10Mohms ), L-E and N-E were clear. I connected the circuit back into the board and just thought id check once more to see if the MCB would reset, and it did. Now i hadnt done any other work other than disconnecting and then reconnecting the circuit from the board prior to my tests. I checked to see if either of the cables were damaged entering the board, wondering if i had inadvertantly disturbed them, but they were fine.

Really struggling to explain this one so any thoughts welcome
 
The only thing you can do is ask your friend to keep a record of when it trips - that said L-N issues tripping a MCB should be easier to find!
 
From your description it is not entirely clear what tripped first.

Did the MCB for the sockets trip - suggesting a L to N fault somewhere?
Or actually did only the 30mA RCD trip, and the MCB was subsequently opened in order to be able to reset the RCD?
 
Can you test the RCDs too?
For what it's worth - I have replaced an mcb which liked tripping without due cause (that I ever found). It's rare though.
 
If it was the MCB tripping that would suggest a L-N fault rather than an earth fault. It's possible that the substantial fault current will have blown the fault clear causing damage if continued attempts were made to reset the mcb.
 
Cannot fathom what was tripping,one of the two RCD's on closing the MCB,or the MCB itself...

It might just be a sign,like was prevalent in the old testament...
 

Reply to RCD tripping, problems identifying fault in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
Replies
4
Views
1K
Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
327
My friend just moved into a new build flat and its for a disabled person with a hydraulic lift to go to the upper floor. There was/is a leak...
Replies
8
Views
441
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
792
I have just checked a double outlet and it trips at 18ma. It was supposed to be faulty. Washing machine had a bad heater which got replaced but...
Replies
10
Views
576

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock