Hello all,

I'm having a problem with a nuisance tripping RCD, ran an RCD test on a board and results showed that RCD was knackered, swapped this out for new and tester again failed to trip the RCD, however customer is telling me of nuisance tripping 6-7 times a day whenever they try to use an appliance.

Is there any fault in a system that could cause an RCD not too trip under test, but yet trip whenever an appliance is being used. I have done all other tests on circuit and all show reasonable results for age of installation.

Thanks,
Gavin
 
Sorry just noticed you tested at board. Try testing at socket outlet, some memshield do not trip if tested at board may have a similar problem.
 
Firstly if your 'new' RCD has failed to trip on testing, you need to be replacing it again...that's obviouslly if you meant it failed to trip at 1x and 5x on both cycles.

Secondly, yes - faulty appliances can take RCD's out...i would advise on PAT testing the appliances that seem to be causing the nuisance tripping.
 
Yes that's exactly what I meant, problem is, it trips with every appliance in the house and the shower, that's why I was wondering whether there was any sort of wiring fault that could cause this problem?
 
that's what i'm thinking. retest RCD with both load L and N dissed. if it trips then, it's a wiring fault, poss. a N-E fault that inhibits your tests but causes tripping when under load.
 
Ze from what I can remember (haven't been there for a few days as customer has been away) is around 0.15ish. There is a circuit in the install which is showing a dead short between all three conductors, although this is obviously switched off in the board, could this fault possibly be the cause of the RCD failing to trip?
 

Reply to RCD tripping problems in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
375
An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
Replies
4
Views
1K
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
850
Cant get my head round this :( I understand N-E faults cause RCD's to trip, but I cant understand why on these 2 occasions, googled allover but...
Replies
13
Views
2K
I'm writing this mainly hoping something occurs to me while writing it! I got called to an occasionally tripping RCD. It's a Hager double height...
Replies
19
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock