Search for tools and product advice,

Discuss RCD Tripping when light is switch off in the UK Electrical Forum area at ElectriciansForums.net

H

hutch6447

Hi, right been to a 3 storey house that has been turned into offices the problem is first all the circuits are protected by 1 RCD the actual fault itself is when you switch the light on in the basement its fine when you turn it off it trips the RCD then everything is off, so I have narrowed it down to the circuit that has the fault on it an isolated it so the rest of the installation is fine.

The circuit that has the problem is a 6A Lighting circuit with 3x lighting points and 2 way switch and an emergency light the occupier said that the in house contractors changed a few lights and did something else.

The bottom switch you can turn that on/off all day and its fine the switch upstairs going on is fine and sometimes it lets you turn it off but other times you turn it off and it trips the RCD, I have tried a new switch that didnt work had a look behind the lights and it seems ok and apparently it all worked fine before the contractors change the lights so to me rules out damaged cable but will do another insulation resistance test on circuit anyway.

Anyone had this problem before? Thanks
 
A double pole 2 way lighting switch. Do they exist?

My bet would be if there was any discharge lighting on the circuit it might cause transient voltages generating an induced voltage on the cpc.
 
Do a full IR test between L/E and N/E when the switch is on and off, it is some leackage there somewhere and sounds like the leakage is in the switch somewhere or even in the wiring between the 2 switches.

Try turning the light one down then coming back up and try the top one. If it only trips in 1 position then its that switch. If it trips in both positions then its the cable between the switches.

Good Luck
 
The circuit that has the problem is a 6A Lighting circuit with 3x lighting points and 2 way switch and an emergency light the occupier said that the in house contractors changed a few lights and did something else.

Like he said - 2 way switch so yes it is a 2 way switch - then yes it has to be a double pole!
 
or two ganged single pole 2-way.

double pole is where two poles are switched at the same time, ie phase and neutral as you would find on an isolator

Edit : an intermediate might fill the part but is still only switching or crossing over one pole.
That would then mean there is another single pole 2-way switch soemwhere.
 
or two ganged single pole 2-way.

double pole is where two poles are switched at the same time, ie phase and neutral as you would find on an isolator

Edit : an intermediate might fill the part but is still only switching or crossing over one pole.
That would then mean there is another single pole 2-way switch soemwhere.

Yes that is what i was alluding too, are both poles switched, i.e Neutral and Line.
 
Switches are generally designed to disconnect the two poles together or the phase a fraction before the neutral.

If there are transient back emfs generated while switching a single pole device then the neutral and/or cpc could carry a current back to the DB
 
Sounds like there is a high standing leakage on one or more of the final circuits and that the switching transients are combining with that to push the leakage over the tripping threshold of the RCD. Solutions:-1) Identify the leakage source(s) and remove or reduce if possible. 2) Remove over all RCD protection and RCBO individual final circuits. 3) Wire a snubber across the offending switch contacts.
 
Hi,

Had a similar problem some years ago with a fluorescent fitting, fine when you turned it on ; blew the fuse ( 3036 ) when you turned it off. Turned out to be the light was one of the one's you could buy back then without a capacitor ( similar to what was used on lead /lag circuits ). Worth a check anyway,

Regards.
 
Yeah narrowed it down to the switch lead going into the plug & play there was a snipped part of the cable just before it entered the plug & play but was not fully broke, probably way it was sometimes ok and other times not. Isolated switch lead and going to run a new lighting circuit for the light.

- - - Updated - - -

Yeah narrowed it down to the switch lead going into the plug & play there was a snipped part of the cable just before it entered the plug & play but was not fully broke, probably way it was sometimes ok and other times not. Isolated switch lead and going to run a new lighting circuit for the light.
 
You are right - double pole is an intermediate switch or a main switch or FSU for example
2 way is a light switch.

I think that comment is wrong I would never class an intermediate switch as a double pole all the do is connect opposite connections together in either of these patterns II X please correct me if I am wrong ?
 
An intermediate switch is anything but double pole, it functions as vjsmarwick says. A 2 way switch isn't double pole either. Light switch are generally single pole.

Intermediate switch

intermediate_sw1.gif


2 way
images.jpg
 
Just out of interest how many computers have they got running? They do like to 'leak' a little bit...
 

Reply to RCD Tripping when light is switch off in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, I swapped a 2 gang switched socket for a 2 gang switchless socket with usb ports downstairs. I switched off all the power to the house by...
Replies
8
Views
823
An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
Replies
4
Views
1K
I sorted the fault fairly quickly as it happens but only because I'd come across it once before and at the time a few people said it couldn't...
Replies
13
Views
387
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
864
Cant get my head round this :( I understand N-E faults cause RCD's to trip, but I cant understand why on these 2 occasions, googled allover but...
Replies
13
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top