M

matt12321

Quick question to all

ive got and Rcd that trips out randomly through the day. Split board and the Rcd covers shower and sockets. With the shower breaker off an the other 4 socket breakers on, the Rcd will trip when u plug a tester in. However when u turn them all off a test each circuit individually the Rcd doesn't trip. Found the circuit it trips on but it only trips with all breakers on. Megger want even test as it trips before a reading is given


any ideas thanks
 
dead testing procedures to start with. then leakage tests.
 
As Tel says, do the tests. I wouldn't worry about which combination of MCB's being on causes the tripping, it will just sidetrack you. RCD's need a load going through them to allow then to trip, it may be some of the circuits have little or no load. Also tripping an MCB doesn't clear an insulation/earth leakage fault because only the live leg is switched so the RCD still has the circuit neutral connected to it.
 
Quick question to all

ive got and Rcd that trips out randomly through the day. Split board and the Rcd covers shower and sockets. With the shower breaker off an the other 4 socket breakers on, the Rcd will trip when u plug a tester in. However when u turn them all off a test each circuit individually the Rcd doesn't trip. Found the circuit it trips on but it only trips with all breakers on. Megger want even test as it trips before a reading is given


any ideas thanks

Run that one by me again will you?
 
When u do X1 or x5 Rcd test at socket the Rcd trips before any normal reading or Rcd fail shows

test it directly in the consumer unit, with circuits disconnected.
it may be over sensitive but more likely theres earth leakage and RCD is just doing its job , leakage clamp meter comes handy for this situations.
 
How long ago was the CU installed and / or the fault occur?

What are the IR readings for the individual circuits covered by said RCD?

Are the other circuits on the other "side" of the CU OK?
 
Last edited by a moderator:

Reply to Rcd tripping in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
Replies
4
Views
1K
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
780
Hi all, There's 2 single fan ovens in the house my mother recently moved into. Posh elecronic AEG units. It's been sat empty for a year, so the...
Replies
19
Views
1K
Hi, I swapped a 2 gang switched socket for a 2 gang switchless socket with usb ports downstairs. I switched off all the power to the house by...
Replies
8
Views
772
Cant get my head round this :( I understand N-E faults cause RCD's to trip, but I cant understand why on these 2 occasions, googled allover but...
Replies
13
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock