Discuss RCD tripping in the Australia area at ElectriciansForums.net

T

Tinyotall

Help Please!!

Had an issue today where a external DBs RCD in a garden shed / workshop keeps tripping. It only trips when high wattage items are used, otherwise its fine. The installation has been active and fine for the past 7 years. I have tested all circuit, all sockets / points but can still not find the fault. the SWA to the shed also tests fine. Any help would be good.......
 
You mention "high wattage items".

Is there a possibility of accumulative leakage from these items???

Is it possible the RCD has deteriorated, have you tried ramp testing it to see at what value it is operating at???
 
You mention "high wattage items".

Is it possible the RCD has deteriorated, have you tried ramp testing it to see at what value it is operating at???
The items are a Heavy duty Vac and a Shower also sometimes trips with the TV turning on. Did change the RCD but no avail. have tried all circuits turn and tried the items in turn in each circuit. gone through every test my Fluke will allow. still scratching head.
 
Could be a faulty batch. Ramp test it and prove it's too sensitive. Then if it proves to be ok, check neutral connections in the CU. Neutral bar and all main neutral lead terminations in main incommer and RCD/RCBOs.
The power to the shed is fed from the meter into a 30amp fused switch then via the SWA to the shed DB.... The only neutral not checked is in on the switch before the SWA, but as this if fed direct from the meter did not want to open it up!
 
not the cheapest solution, but you could replace the MCbs with RCBOs, ditch the existing RCD. that should track the fault down to 1 circuit.
 
Higher current makes me think more earth leakage. What were your IR values on those circuits?

Edit: have the appliances that are causing the tripping been tested?
 
Last edited by a moderator:
Help Please!!

Had an issue today where a external DBs RCD in a garden shed / workshop keeps tripping. It only trips when high wattage items are used, otherwise its fine. The installation has been active and fine for the past 7 years. I have tested all circuit, all sockets / points but can still not find the fault. the SWA to the shed also tests fine. Any help would be good.......

That would say to me one or two things there as been a deterioration of the installation or there is something new that as been introduced.

As you say you have replaced the RCD with another and still the same. You have checked the terminations all ok, so is there a dampness issue, I assume the shed is also 7+ yrs old could there be a breakdown in insulation that is causing dampness, to check this you could for a temp test do away with RCD protection and see what happens, you will though need to make sure that your ZS for the protection devices are spot on.

Second then if all this is ok is anything new bought, or is there an intermittent fault on existing appliance ie is the shower element breaking down. If you have bought a new piece of equipment then maybe that is having a cumulative affect on protective conductor current so check that with an appropriate clamp meter. IF all Ok then start to PAT test the appliances.
 
and if all else fails. --- wooden shed... bonfire night next month.......
 
That would say to me one or two things there as been a deterioration of the installation or there is something new that as been introduced.

As you say you have replaced the RCD with another and still the same. You have checked the terminations all ok, so is there a dampness issue, I assume the shed is also 7+ yrs old could there be a breakdown in insulation that is causing dampness, to check this you could for a temp test do away with RCD protection and see what happens, you will though need to make sure that your ZS for the protection devices are spot on.

Second then if all this is ok is anything new bought, or is there an intermittent fault on existing appliance ie is the shower element breaking down. If you have bought a new piece of equipment then maybe that is having a cumulative affect on protective conductor current so check that with an appropriate clamp meter. IF all Ok then start to PAT test the appliances.

Many thanks for all input. Have narrowed down the issue to the shower, did pat test it and it failed on leakage.
 

Reply to RCD tripping in the Australia area at ElectriciansForums.net

Similar Threads

An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
Replies
4
Views
1K
Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
329
Cant get my head round this :( I understand N-E faults cause RCD's to trip, but I cant understand why on these 2 occasions, googled allover but...
Replies
13
Views
1K
My circuit panel has two banks of breakers, each bank protected by an RCD. One of these RCDs has been problematic in that it trips intermitantly...
Replies
12
Views
1K
Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock