Discuss RCD Tripping in the UK Electrical Forum area at ElectriciansForums.net

H

hutch6447

Hello guys had a lady on the phone who said she has upstairs and downstairs ring mains, she can plug the 1400 watt vac in upstairs and its fine but she cant plug it in downstairs as it trips the RCD protecting it I am not sure never come across this?
 
Could just be that one RCD is more sensitive than the other. Tests will show.

Either way, sounds like the Vacuum sucks.
 
This is becoming a more recurrent theme: nuisance RCD tripping through nothing more than electrical accumulation. I'll often clamp a 'perfectly good' domestic installation's tails and see the other side of 40mA+ leakage, through all the digital stuff plugged in.

What's the betting that next set of regs will have us all installing RCBO's and doing away with the split board??
 
Yes accumulation of leakage is becoming a large thing now, as you say all these digital appliances its not rare to see high leakage. I find where possible to use Rcbos they are so much better but the price of a loaded rcbo board doesn't bare thinking about!
 
Hello guys had a lady on the phone who said she has upstairs and downstairs ring mains, she can plug the 1400 watt vac in upstairs and its fine but she cant plug it in downstairs as it trips the RCD protecting it I am not sure never come across this?

did u ask the caller if upstairs ring is on the rcd??
 
Yes went round to look the kitchen and living room are on one ring main downstairs and upstairs is on another now everything works fine except when youplug the vacuum into a socket in the living room it trips the RCD but plug it into the kitchen it also works fine, the vacuum is 1400 watt dyson but plug the kettle (2300 - 3000 W) into the living room sockets and it works fine not come across this in the forces I tell you. The installation is on a split double RCD board.
 
Last edited by a moderator:
Done a full test and everything was spot on, did ramp test on rcd's and one was significantly more sensitive so replaced it and everything is fine.
 

Reply to RCD Tripping in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi Guys, I'm having trouble diagnosing a fault on a customers downstairs socket ring, which only ever trips when the washing machine is used. The...
Replies
22
Views
3K
Good day. First time poster. We recently had an electrician perform the EICR, as this is a newly purchased property I thought'd I would have the...
Replies
7
Views
765
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K
Woke up this morning and tried to turn on the computer (work from home) wouldn't power on, checked lights they worked fine. Went downstairs to...
Replies
21
Views
3K
Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock