Discuss RCD trips with all load breakers open in the DIY Electrical Advice area at ElectriciansForums.net

santoli3

DIY
Reaction score
5
My circuit panel has two banks of breakers, each bank protected by an RCD. One of these RCDs has been problematic in that it trips intermitantly. A few months ago it became so frequent that we had the RCD replaced. It would trip regardless of what load breakers were shut or open. No fault could be found at the time. It was fine affter replacement until today. Today it tripped, and will only reset for a short period of time before tripping again. It trips even if all of the downstream load breakers are open. I don't understand what fault could result in a trip when all of the load breakers are open. Since there is no current, there can be no current imbalance between earth and neutral. What am I missing?
 

Attachments

  • 20230922_182132.jpg
    126.8 KB · Views: 11
Could there be some N current from one of the unprotected circuits finding it's way to the N of an RCD-protected circuit?
 
The circuit breakers for your final circuits are all single pole which means when they are open only the line (brown) is disconnected from the rcd, the neutral (blue) remains connected. I suspect a neutral to earth fault but before jumping the gun you should call in a good electricians with the appropriate skill and test equipments to do some dead tests and visual inspections of all the final circuits of your CU. Ask him/her also to check the tightness and solidity of all connections.

Note that the fault could be with a load plugged in or permanently wired in and not with the circuit supplying the power to it so your loads should be tested too.
 
As per Marconi above, an experienced electrician should be able to track the problem down.

In my (admittedly limited) experience, immersion heaters and appliances, particularly those heating water, can develop earth leakage of their heating elements. As an experiment, you could try switching off your immersion heater at its own switch, which should be double pole, and/or completely unplugging the washing machine and anything else in the utility room that would fit into the category above. That way you disconnect their neutrals, which usually don't get isolated if turning off at the plug.
It's a long shot, and probably won't locate the problem, but it's something else to try!
NB having second thoughts on the above, because if the RCD's still tripping with all the mcb's off, it's probably not the above 🤔
 
The circuit breakers for your final circuits are all single pole which means when they are open only the line (brown) is disconnected from the rcd, the neutral (blue) remains connected. I suspect a neutral to earth fault but before jumping the gun you should call in a good electricians with the appropriate skill and test equipments to do some dead tests and visual inspections of all the final circuits of your CU. Ask him/her also to check the tightness and solidity of all connections.

Note that the fault could be with a load plugged in or permanently wired in and not with the circuit supplying the power to it so your loads should be tested too.
Thanks Marconi. I get that. But with all of the load breakers open, there is no current going to any of the loads. So there is zero current on the line side of the RCD. But with no current going to any of the loads, there can be no current coming back through neutral from the loads either, and therefore zero current on the neutral side of the RCD. Two zeros = no imbalance. I know I’m missing something. But what?
 
As per Marconi above, an experienced electrician should be able to track the problem down.

In my (admittedly limited) experience, immersion heaters and appliances, particularly those heating water, can develop earth leakage of their heating elements. As an experiment, you could try switching off your immersion heater at its own switch, which should be double pole, and/or completely unplugging the washing machine and anything else in the utility room that would fit into the category above. That way you disconnect their neutrals, which usually don't get isolated if turning off at the plug.
It's a long shot, and probably won't locate the problem, but it's something else to try!
NB having second thoughts on the above, because if the RCD's still tripping with all the mcb's off, it's probably not the above 🤔
Yeah, It's the trippimg no matter what breakers are shut, and even when all are open that is really confusing me.
 
Could there be some N current from one of the unprotected circuits finding it's way to the N of an RCD-protected circuit?
Well, they are all protected. But they are in two banks, each bank with an RCD.
 
If the neutral and earth conductors have a potential difference between them where they enter your property, and this pd could depend on network neutral current then even in absence of line current through the rcd there may well be a neutral current flowing ‘forwards’ through the rcd and then via an rcd load side n-e fault and then all the way back via e conductor or terra firma to the supply transformer star point which is where the network earthed neutral originates. Thus an unbalance of current through the rcd happens. A loop circuit with an emf in it causes a current to flow through the loop.

Shows us a picture of your supply intake so we can work out your home’s earthing system please.
 
As per Marconi above, an experienced electrician should be able to track the problem down.

In my (admittedly limited) experience, immersion heaters and appliances, particularly those heating water, can develop earth leakage of their heating elements. As an experiment, you could try switching off your immersion heater at its own switch, which should be double pole, and/or completely unplugging the washing machine and anything else in the utility room that would fit into the category above. That way you disconnect their neutrals, which usually don't get isolated if turning off at the plug.
It's a long shot, and probably won't locate the problem, but it's something else to try!
NB having second thoughts on the above, because if the RCD's still tripping with all the mcb's off, it's probably not the above 🤔
You are on the right track, add to the list of usual suspects
Electric oven, grill and of course any outdoor lights or sockets
 

Reply to RCD trips with all load breakers open in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

Hi I am asking for help as a novice and 1st time user of this forum. Recently started to experience tripping of MCB & sometimes with the RCD at...
Replies
7
Views
598
Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K
Background Two weeks ago, lightning struck a tree in our yard. Many circuits tripped and several electronic devices failed. There was a strong...
Replies
2
Views
896
Hi all. We have a 120v 20 amp circuit to an accessory dwelling with a run of about 75' of direct bury #12. The breaker keeps tripping even when...
Replies
3
Views
330
I'm not an electrician. I clean cookers and today arrived to a rangemaster range cooker. Got started, and as part of my routine, I turn on ovens...
Replies
1
Views
821

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock