If the neutral and earth conductors have a potential difference between them where they enter your property, and this pd could depend on network neutral current then even in absence of line current through the rcd there may well be a neutral current flowing ‘forwards’ through the rcd and then via an rcd load side n-e fault and then all the way back via e conductor or terra firma to the supply transformer star point which is where the network earthed neutral originates. Thus an unbalance of current through the rcd happens. A loop circuit with an emf in it causes a current to flow through the loop.

Shows us a picture of your supply intake so we can work out your home’s earthing system please.
OK. Based on that discussion, I took measurements of neutral bus to earth on each side, and I think I've sorted it. I opened the panel, and opened the main, both RCDs and all load breakers. The attached picture was taken just prior to opening all breakers. Then I measured neutral bus to earth bus resistance on both sides. The left side was overload. The right side was 20 Ohms. I then disconnected individual neutrals one at a time on the right neutral bus until the right side went to overload. It turns out the immersion heater is the culprit. I left disconnected the immersion heater neutral and insulated it. I also disconnected the immersion heater load side from its breaker and insulated it. I labeled both as “Immersion Heater – Faulted”. Now with both sides OL to earth, I buttoned it up and shut all the breakers. So far so good. Thanks all!20230923_130937.jpg
 
Last edited by a moderator:
OK. Based on that discussion, I took measurements of neutral bus to earth on each side, and I think I've sorted it. I opened the panel, and opened the main, both RCDs and all load breakers. The attached picture was taken just prior to opening all breakers. Then I measured neutral bus to earth bus resistance on both sides. The left side was overload. The right side was 20 Ohms. I then disconnected individual neutrals one at a time on the right neutral bus until the right side went to overload. It turns out the immersion heater is the culprit. I left disconnected the immersion heater neutral and insulated it. I also disconnected the immersion heater load side from its breaker and insulated it. I labeled both as “Immersion Heater – Faulted”. Now with both sides OL to earth, I buttoned it up and shut all the breakers. So far so good. Thanks all!
Well done! Worth checking at the immersion heater (preferably with the local switch 'off') the resistance between the element connections and ground. Sounds like you need a new one!
 
Well done! Worth checking at the immersion heater (preferably with the local switch 'off') the resistance between the element connections and ground. Sounds like you need a new one!
Thanks. Need is a strong word. The immersion heater breaker hasn't been shut since we moved in (maybe the previous knew something). So I certainly don't need it. But I did rethink my solution, and disconnected the immesion heater loacaly, insulated the leads, and labeled the cover "Immersion heater disconnected due to earth fault". I then reconnected everything in the breaker panel, checked that neutral to earth was still good, then labeled the breaker "immerion heater faulted". This way, the next person to live here, if they "need" the immersion heater, can sort it without having to enter the breaker panel.
 

Reply to RCD trips with all load breakers open in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

Hi I am asking for help as a novice and 1st time user of this forum. Recently started to experience tripping of MCB & sometimes with the RCD at...
Replies
7
Views
598
Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K
Background Two weeks ago, lightning struck a tree in our yard. Many circuits tripped and several electronic devices failed. There was a strong...
Replies
2
Views
896
Hi all. We have a 120v 20 amp circuit to an accessory dwelling with a run of about 75' of direct bury #12. The breaker keeps tripping even when...
Replies
3
Views
330
I'm not an electrician. I clean cookers and today arrived to a rangemaster range cooker. Got started, and as part of my routine, I turn on ovens...
Replies
1
Views
821

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock