OK. Based on that discussion, I took measurements of neutral bus to earth on each side, and I think I've sorted it. I opened the panel, and opened the main, both RCDs and all load breakers. The attached picture was taken just prior to opening all breakers. Then I measured neutral bus to earth bus resistance on both sides. The left side was overload. The right side was 20 Ohms. I then disconnected individual neutrals one at a time on the right neutral bus until the right side went to overload. It turns out the immersion heater is the culprit. I left disconnected the immersion heater neutral and insulated it. I also disconnected the immersion heater load side from its breaker and insulated it. I labeled both as “Immersion Heater – Faulted”. Now with both sides OL to earth, I buttoned it up and shut all the breakers. So far so good. Thanks all!If the neutral and earth conductors have a potential difference between them where they enter your property, and this pd could depend on network neutral current then even in absence of line current through the rcd there may well be a neutral current flowing ‘forwards’ through the rcd and then via an rcd load side n-e fault and then all the way back via e conductor or terra firma to the supply transformer star point which is where the network earthed neutral originates. Thus an unbalance of current through the rcd happens. A loop circuit with an emf in it causes a current to flow through the loop.
Shows us a picture of your supply intake so we can work out your home’s earthing system please.