Discuss RCD types and DC current in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
113
So, this article https://electrical.------.org/wirin....org/wiring-matters/issues/77/which-rcd-type/ seems to suggest we should install a type F RCD wherever a washing machine is found (among other things). Is anyone actually doing this? If not, how do we justify not doing? Both BG & Wylex CUs at Screwfix both still come with AC RCDs as far as I can see. Further, most appliances in domestic premises are plugged in, so how can we have any idea what might be used there, and so whether it might produce DC fault currents?
[automerge]1575729733[/automerge]
The link is being changed when I post and so is not working. The article can be found on the IET's website under
  • Wiring Matters
  • Years
  • 2019
  • 77 - September 2019
  • Which RCD Type?
 
e5 have done some brilliant podcasts and videos on YouTube regarding this, well worth checking out.
Wiring matters had an article in around the end of 2017 about RCDs and since reading that I've been installing A type RCDs, and since the 18th I've only installed RCBO CUs I've never installed a F type or a B type yet, but I'm aware that some washing machines with synchronous motors state that they need protecting against a high frequency leakage, which can render normal RCDs useless.

John Ward has also done some brilliant videos about the effects of pulsed DC on AC RCDs.
I think in due course AC RCDs will be non compliant like they are in some other European countries.
 
... I'm aware that some washing machines with synchronous motors state that they need protecting against a high frequency leakage, which can render normal RCDs useless.
Only the appliance manufacturer would know if they are using D.C and there's a fault risk, much like Electric Vehicle charging.

These points kind of illustrate my thinking: are we really supposed to read the manuals of all the appliances in a house before specifying RCDs? Is anyone doing that? And with the best will in the world, we could go into a house with a twin-tub, fit AC RCDs, then next week the customer buys a brand new washing machine with all the electronics and high-frequency leakage.

AJShep I will have a look for those videos, thanks.
[automerge]1575805120[/automerge]
People have had audiovisuals (electronics) for decades. This starts to look like another example of manufacturers pedalling stuff which is not, and never has been, fit for purpose. ELCBs, plastic consumer units, and now seemingly AC RCDs.
 
e5 have done some brilliant podcasts and videos on YouTube regarding this, well worth checking out.

...

John Ward has also done some brilliant videos about the effects of pulsed DC on AC RCDs.
I think in due course AC RCDs will be non compliant like they are in some other European countries.

Some very good videos, thanks. Looks like I may be fitting more A type RCDs in future. It's just a shame all the dual RCD consumer units (except perhaps Hager) seem to come with AC type. I might also make a habit of watching the e5 channel and JW too.
 
e5 have done some brilliant podcasts and videos on YouTube regarding this, well worth checking out.
Wiring matters had an article in around the end of 2017 about RCDs and since reading that I've been installing A type RCDs, and since the 18th I've only installed RCBO CUs I've never installed a F type or a B type yet, but I'm aware that some washing machines with synchronous motors state that they need protecting against a high frequency leakage, which can render normal RCDs useless.

John Ward has also done some brilliant videos about the effects of pulsed DC on AC RCDs.
I think in due course AC RCDs will be non compliant like they are in some other European countries.

I too no longer install dual RCD boards, having switched to A type RCBOs since the 18th edition came into effect. Apart from the better protection that A type RCBOs offer, fitting these RCBOs will ensure that regulations 531.3.2, 536.4.3.2 and 536.4.202 are complied with.

I think the AC type RCD has had its day and is now all but redundant. I expect these devices to be phased-out in due course, perhaps around the same time as the IET eventually decide to make AFDDs compulsory, as no doubt they surely will.
 

Reply to RCD types and DC current in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello! I've been racking my brain this evening about some RCD selections. I've been doing some work for a solar installer, and they've asked me...
Replies
5
Views
977
I decided to get solar panels, the inverter instructions say one can use type AC, so the existing 14 x RCBO CU seems OK, may be a good idea to fit...
Replies
4
Views
2K
Hello All, I am a homeowner (but not an electrician) and I am renovating a house that has an old CU containing MCBs and an MK LN5725 residual...
Replies
5
Views
859
I have been asked/invited to "post more", lol, so let me make another post right away. I thought of sth worthy to post, of interest to many, I...
Replies
2
Views
499
A friend of mine asked me to look at here PV system as she is not getting any power (and thus money) from it. First real issue is the Aurora...
Replies
8
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock