Discuss Rcds not tripping at 50ms now in the Electrician Courses : Electrical Quals area at ElectriciansForums.net

Wilson12

-
Trainee
Reaction score
3
Hello
I've got a rcd
It trips at 1 times okay but gets greater than 50ms at 5x on one cycle but it's okay on the other cycle on three rcbos out of 5 it's not the circuit I've swapped over the cable what's that mean what will happen
 
1st try a different tester. if still > 40mSec. @ x5, then it's a failed RCD, but be sure to test without the outgoing RCD terminals NOT connected to circuit/s.
 
As said, make sure your outgoing circuits are disconnected and re-test.
Over 40ms @ 5x is not compliant.

What make are the RCBOs ?
 
Hello
I've got a rcd
It trips at 1 times okay but gets greater than 50ms at 5x on one cycle but it's okay on the other cycle on three rcbos out of 5 it's not the circuit I've swapped over the cable what's that mean what will happen
1 RCBO is suspect
2 Change RCBO
 
It has all been said above.
If the RCD does not work it has failed, but eliminate the possibility of the attached circuit affecting the RCD before you just change it, especially as you have this on three RCDs.
 
and if you can't fix it with a hammer, it's definitely an electrical problem.
 

Reply to Rcds not tripping at 50ms now in the Electrician Courses : Electrical Quals area at ElectriciansForums.net

Similar Threads

I have just checked a double outlet and it trips at 18ma. It was supposed to be faulty. Washing machine had a bad heater which got replaced but...
Replies
10
Views
568
An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
Replies
4
Views
1K
Hi all, There's 2 single fan ovens in the house my mother recently moved into. Posh elecronic AEG units. It's been sat empty for a year, so the...
Replies
19
Views
1K
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
780
Hello! I've been racking my brain this evening about some RCD selections. I've been doing some work for a solar installer, and they've asked me...
Replies
5
Views
891

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock