Cant quite get my head around how you use this reg?
Lets say S =16
I = 657
k = 115
You have to work out t first of all so
t = K[SUP]2[/SUP]S[SUP]2[/SUP]/I[SUP]2
[/SUP]so t = 7.843409 (to 6dp)
therfore K[SUP]2[/SUP]S[SUP]2[/SUP] = 3385600
The reg says that we need to make sure that K[SUP]2[/SUP]S[SUP]2 [/SUP]is greater than the value of the let through energy (I[SUP]2[/SUP]t),
But using the above equation I[SUP]2[/SUP]t also equals 3385600.
By using the above equation they will ALWAYS equal each other as your just messing around with the same equation.
I read the reg as K[SUP]2[/SUP]S[SUP]2 [/SUP]having to be greater than I[SUP]2[/SUP]t as it says:
'for current limiting devices K[SUP]2[/SUP]S[SUP]2 [/SUP]shall be greater than the value of the let through energy I[SUP]2[/SUP]t',
Bit confusing?