Discuss regulation for 80amp fuse and 16mm meter tails in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

T

topcat72

Clarifiation please !

I have read somewhere, maybe in BS7671 or on a forum site regulation that states that 16mm meter tails can or should be used on supplies rated at 80amps or under and 25mm tails on supplies rated at 100amps.

I have scoured BS7671 and various forums but cannot find this regulation, have I seen this, does such a regulation exist ?

As the current carrying capacity of a 16mm meter tail Is 87amps it would make sense or is this just common practice

Thanks in advance

TC
 
Clarifiation please !

I have read somewhere, maybe in BS7671 or on a forum site regulation that states that 16mm meter tails can or should be used on supplies rated at 80amps or under and 25mm tails on supplies rated at 100amps.

I have scoured BS7671 and various forums but cannot find this regulation, have I seen this, does such a regulation exist ?

As the current carrying capacity of a 16mm meter tail Is 87amps it would make sense or is this just common practice

Thanks in advance

TC
follow the tables in bs7671 and you cant go wrong.

most people install 25mm simply because usually the fusecarier can only take a max 100amp fuse unless its replaced with a slow blow
 
Clarifiation please !

I have read somewhere, maybe in BS7671 or on a forum site regulation that states that 16mm meter tails can or should be used on supplies rated at 80amps or under and 25mm tails on supplies rated at 100amps.

I have scoured BS7671 and various forums but cannot find this regulation, have I seen this, does such a regulation exist ?

As the current carrying capacity of a 16mm meter tail Is 87amps it would make sense or is this just common practice

Thanks in advance

TC
the only info i have found atm in byb is 16mm copper and 25mm ali is the minimum p133
 
Last edited:
Clarifiation please !

I have read somewhere, maybe in BS7671 or on a forum site regulation that states that 16mm meter tails can or should be used on supplies rated at 80amps or under and 25mm tails on supplies rated at 100amps.

I have scoured BS7671 and various forums but cannot find this regulation, have I seen this, does such a regulation exist ?

As the current carrying capacity of a 16mm meter tail Is 87amps it would make sense or is this just common practice

Thanks in advance

TC

The cable size should be calculated in the same way as all other cable sizes are, though it is safe not to worry about VD at that length.
 
personally id change them to 25mm but your right 16mm is ok for 80amp my tails in my house are 25mm but the dnos are 16mm so when they were changing my meter to one of these smart ones i ask him how come my tails have to be 25 and yours are 16 makes no sence he said we work to different reqs ha ha bull ****
 
personally id change them to 25mm but your right 16mm is ok for 80amp my tails in my house are 25mm but the dnos are 16mm so when they were changing my meter to one of these smart ones i ask him how come my tails have to be 25 and yours are 16 makes no sence he said we work to different reqs ha ha bull ****
not really, we work to bs7671. they dont, they work to a different guide book
 
I agree that if we are being told to upgrade tails, then the meter installers should replace them too.

That said, changing tails should be based on the situation, including length, reference method and potential load.
 
CPR got it ... changing tails are subject to the same calcs and rules as any cable throughout an install and its this that denotes the size... the 25mm is a safeguard as we legally do not have access to the DNO cutout fuse rating and as in most domestic this is inside a 100amp rated carrier then we are to assume it for a max rated fuse.
If you have knowledge of a lower rated fuse then that can be used for your design and thus in your situe be 16mm.
 
The Best Practise Guide for domestic consumer unit change (number 6) says on page 5 (note 4 I think) that you can keep the 16mm tails even if there is a 100A cut out fuse..... as long as it meets reg 434.5.2 (i.e K[SUP]2[/SUP]S[SUP]2[/SUP] is greater than I[SUP]2[/SUP]t) AND your max demand is less then the CCC of the 16mm tails.
 
Where the majority of domestic installs are concerned the chances of overloading a 16mm 1 meter or less, set of supply tails is very unlikely.
These days its the modern showers that are probably the heaviest appliance loads followed by kitchen cooking equipment hobs and the like.
None of which are pulling current for long enough to cause issues.
The only time I have seen problems have been in commercial settings, and usually down to poor or loose connections.
Certainly helps to explain why in the real world you wont see many heat damaged 16mm tails even if they are paired with a 100 amp cut out fuse.
 
Another IMHO valid point is one of flexibility and practicality when working 25mm into a single screwed soft material clamping point.
Those not so sturdily manufactured plastic mains isolators can be very unforgiving and with plastic din mounts and often limited access space in some of these domestic c/u's. 16mm can often result in less mechanical strain and a superior clamp connection.
A good tight connection that's not subject to mechanical strain is as far as I am concerned more important when it comes to the possibility of heat or thermal damage to tails.
In real world scenario it doesn't take a lot to work a 25mm tails loose in those isolators compared to 16mm.
So your damned if you do and damned if you don't.
Oh well !! we can cover the problem up in metal enclosures soon so whoopie dee.
 

Reply to regulation for 80amp fuse and 16mm meter tails in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Evening, Carried out EV charger installation survey today & found this meter. Is that a 16mm concentric type cable adapter between cutout &...
Replies
16
Views
6K
Hi guys, I hope you're all doing ok in this heat!! I have recently carried out an EICR on a domestic property where it failed miserably. The...
Replies
6
Views
6K
Hi, Just had a new Smart Meter fitted yesterday along with isolator. The chaps installing the SMART meter used 16mm tails from the main DNO fuse...
Replies
16
Views
8K
Hello All, new to the forum. Would be grateful for advice on whether the following proposal is an acceptable solution or open to any suggestions...
Replies
9
Views
5K
Hi I don't know if I should ask it here or the main electricians forum. It's about CU change and the work around it and the CU change will be done...
Replies
78
Views
11K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock