It looks like 6.0 from the head so that will need changing to 16.0. You can then put a small 4 way block in and reduce to 10.0 as circuit protection is then provided by the 60A fuse, put a Safety Electrical Connection-Do Not Remove notice by it. The only problem here is breaking the seal on the head, some may argue the 6.0 is fine but it is inadequate to support the new bonding. If I was assessing I would definitely question using a dual board on those limited circuits, use separate rcbos, in fact you can say to the assessor you chose this method as it provides better division of circuits, not many people would quote this.
Wylex person myself but would avoid MK at all costs.