Discuss Relay switching max voltage across contacts in the Industrial Electricians' Talk area at ElectriciansForums.net

plugsandsparks

-
Esteemed
Arms
Reaction score
2,026
Thought i would put this out there for any experience faced with this design issue.

TP Immersion heater 11KW, has built in contactor, coil voltage 400V
I want to bring in the immersion heater via control system and ideally not alter the immersion heater package.
The control system can operate a volt free contact which i could use to switch the 400V coil.
However, the control system manufacturer does not quote a max switching voltage, all its data is for 230V .
Now i know the current will be tiny but nethertheless there will be 400V across the relay contacts.
I can install another relay from RS that at least does quote a 450V max switching voltage but that would mean i have a control relay, switching a "special relay" that then brings in the immersion contactor.

Would you go with just the std relay and hope 400V will not harm it or would you put another relay in for comfort.
Yes i know the logical thing is to alter the coil voltage to 230V but that is not preferred ATM.

Any help / experience gratefully received

thx
P&S
 
I would definitely add an interposer relay properly rated for 400V. Many small relays of the type used for volt-free outputs have contacts rated for 250V maximum, so in the absence of other information that is what I would expect. Although as you say the contactor coil power is small and it would probably work (possibly with the aid of a snubber or VDR) I would not consider it adequate unless sanctioned by the manufacturer. Plus you would be applying 400V across PCB creepage distances that might not be designed for it, increasing the risk of flashover or carbonisation if it gets damp etc.
 
I would definitely add an interposer relay properly rated for 400V. Many small relays of the type used for volt-free outputs have contacts rated for 250V maximum, so in the absence of other information that is what I would expect. Although as you say the contactor coil power is small and it would probably work (possibly with the aid of a snubber or VDR) I would not consider it adequate unless sanctioned by the manufacturer. Plus you would be applying 400V across PCB creepage distances that might not be designed for it, increasing the risk of flashover or carbonisation if it gets damp etc.
Thx LN, found a relay DIN rail , tiny and rated at 450V for £13, not worth the risk as your head is where my fears lay. Appreciate feedback
 
Somebody is presumably paying for your professional expertise and you suggest that hoping 400V won't harm the contacts is a design option, despite the manufacturers data sheet telling you otherwise. Hard to believe when the correct solution is easy and cheap to implement.
 
@LN, well eventually i found the ideal solution. ABB had the answer. They were the only control system manufacturer that i could find that published the various voltages and loads across the industry standard of 250 and 440V along with currents for AC1 and AC3 and loads of data on capacitive loads. Its a shame that Gira and Theben do not give more design info around their switching capability.

I think i have now justified my colossal design fee...lol

One less component now in the system.

 

Reply to Relay switching max voltage across contacts in the Industrial Electricians' Talk area at ElectriciansForums.net

Similar Threads

Good evening! Don’t have a huge deal of experience with fire alarms but having to work on a conventional system at the minute with various...
Replies
8
Views
590
I previously posted about having a single phase reversing motor which I thought had a centrifugal switch. After looking into it more, it actually...
Replies
1
Views
1K
  • Sticky
Ferrets are known for being small, resourceful, and incredibly clever. They can solve many problems by fitting into tight spaces and doing jobs us...
Replies
4
Views
2K
I have a bathroom fan with a moisture detector that turns it on and off. It also has a control circuit to turn it on/off when moisture is not...
Replies
1
Views
255
Hi all I am new to this forum and hope this is right placed and of interest. I would like to make a setup with one or more impulse relays...
Replies
9
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock