Discuss Relay Wiring in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

P

Phillay

Hi guys, need some advice.

Have a condensate pump to wire up. The pump has a safety switch cable (1 blue, 1 brown wire) that is to be wired into the 'permanent live' to a combi boiler. Therefore, if pump failure occurs, the combi will be shut down (as it condenses in both H and DHW).

The cable size of the safety switch is 0.5mm... but the boiler manufacturers have specifically stated the power to the boiler must by wired from the 3 amp fuse in 0.75mm and it's not acceptable to drop to 0.5mm to incorporate the switch.

Can't upgrade the safety switch cable and so the boiler manufactures have suggested I could use a relay to supply the boiler and the condense safety switch cuts the relay if pump failure occurs (this will mean the boiler is still continuously fed by 0.75mm).

Been putting this off for a while as I haven't got a clue as to what type of relay to use and how this would be wired up.

Cheers.
 
What Boiler is it?

I can't see the condensate switch being used to isolate the power to the boiler as that would prevent pump over-run to cool the heat exchanger down.

I would have thought it would just have safety circuit connection to inhibit the burner.
 
Boiler is Worcester Bosch Greenstar Compact. Worcester themselves advised:

"[FONT=&quot]You would need to have the pump wired into permanent supply to the boiler so if there was a failure the boiler would be isolated completely making it impossible to produce any more condense. Having it wired across the LS & LR connections would mean that the boiler would not fire for heating but it would for hot water, so the boiler would still be producing condense which could back up to the boiler and given enough time cause damage to the boiler."[/FONT]
 
What Boiler is it?

I can't see the condensate switch being used to isolate the power to the boiler as that would prevent pump over-run to cool the heat exchanger down.

I would have thought it would just have safety circuit connection to inhibit the burner.

It's a combi boiler, there's no way to inhibit the burner without altering the internal wiring of the boiler.
 
Just to clarify (incase I haven't!), the safety switch on the condense pump will only operate (break the circuit) in the event of a the pump water level getting too high.
 
Doesn't appear they do... it's pretty frustrating really.

Worcester state the cable from spur to boiler must be a continuous size of 0.75mm, yet it's only on a 3 amp load.

The safety switch cable may only be 0.5mm, but Grundfos install instructions state the safety switch can handle a max of 5 amps.

All in the all, I would expect the 3 amp fuse to blow way before the 0.5mm cable would melt... but Worcester are basically telling me any drop in the cable size is unacceptable and would cause warranty issues.

Nice of them to offer up the idea of a relay, but I'm in the dark on that one.
 
Doesn't appear they do... it's pretty frustrating really.

Worcester state the cable from spur to boiler must be a continuous size of 0.75mm, yet it's only on a 3 amp load.

The safety switch cable may only be 0.5mm, but Grundfos install instructions state the safety switch can handle a max of 5 amps.

All in the all, I would expect the 3 amp fuse to blow way before the 0.5mm cable would melt... but Worcester are basically telling me any drop in the cable size is unacceptable and would cause warranty issues.

Nice of them to offer up the idea of a relay, but I'm in the dark on that one.

0.5mm flex is rated to 3amp
 
0.5mm flex is rated to 3amp

Yeah, that's what I thought... with 0.75mm rated to 6amp.

However, Grundfos install instructions state:

"To shutdown the condensate source (i.e. condensing boiler) the auxiliary contact switch can be utilised. COM1 and NO3 terminals of the overflow switch should be connected in series with the low-voltage thermostat circuit of the boiler. It could also be used to isolate the boiler Live connection providing the current load is no greater than 5 A."

There's no mention of upgrading the cable and it comes wired with 0.5mm... so seems they're suggesting 5 amp can be handled.
 
Yeah, that's what I thought... with 0.75mm rated to 6amp.

However, Grundfos install instructions state:

"To shutdown the condensate source (i.e. condensing boiler) the auxiliary contact switch can be utilised. COM1 and NO3 terminals of the overflow switch should be connected in series with the low-voltage thermostat circuit of the boiler. It could also be used to isolate the boiler Live connection providing the current load is no greater than 5 A."

There's no mention of upgrading the cable and it comes wired with 0.5mm... so seems they're suggesting 5 amp can be handled.

And does your regulations book say anything about the minimum permitted cable size for the wiring of a control system?
 
0.5mm flex is rated to 3amp

Yeah, that's what I thought... with 0.75mm rated to 6amp.

How Grundfos state:

"To shutdown the condensate source (i.e. condensing boiler) the auxiliary contact switch can be utilised. COM1 and NO3 terminals of the overflow switch should be connected in series with the low-voltage thermostat circuit of the boiler. It could also be used to isolate the boiler Live connection providing the current load is no greater than 5 A."

So, although they supply the pump with a 0.5mm safety switch cable that's pre-wired, seems they're suggesting it can take up to 5amps.
 
Didn't think that first post had gone through... sorry for the double post!

Trying to install everything in-line with the manufacturers instructions... it just doesn't appear that the Grundfos pump meets Worcester's demands regards the safety switch.
 
Didn't think that first post had gone through... sorry for the double post!

Trying to install everything in-line with the manufacturers instructions... it just doesn't appear that the Grundfos pump meets Worcester's demands regards the safety switch.

Install a sodding relay as suggested by Worcester
 
Cheers guys...

Never had this problem before...

Evident that my electrical experience as a 'Plumber' doesn't stretch to the understandings of how to incorporate a relay here... when it comes to that, wouldn't know what relay to go out and get.

Will see if Grundfos will take it back, but had it a few months so who knows.... looks like I'll be scanning through the yellow pages for some assistance... safest way to go.

Thanks for your help.
 
Cheers guys...

Never had this problem before...

Evident that my electrical experience as a 'Plumber' doesn't stretch to the understandings of how to incorporate a relay here... when it comes to that, wouldn't know what relay to go out and get.

Will see if Grundfos will take it back, but had it a few months so who knows.... looks like I'll be scanning through the yellow pages for some assistance... safest way to go.

Thanks for your help.

Where are you based? Maybe some one on the forum will be near.
 

Reply to Relay Wiring in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

I am trying to understand how a relay system works and have designed a circuit and a ladder diagram all as attached for an 8 PIN relay, a current...
Replies
2
Views
102
Hi Everyone, New to the forum but hoping I can find a little help with my restoration project... I am adding a secondary wiring "system" to my...
Replies
14
Views
904
Hi all, I need help/feedback. I am modifying a machine. I have added an aluminium profile frame (enclosure ) to a machine (the machine will be...
Replies
2
Views
800
I've always thought I was quite good a wiring heating systems, I can do Y plan, S plan, UFH set ups, "normal" thermal stores etc, you name it and...
Replies
4
Views
951
Hi folks, I'd like to get my Nest thermostat up and running with the gas combi boiler (Worcester Greenstar HIghflow 440 Standalone). FYI - I...
Replies
9
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock