Recently moved into a house from the 70s. There's no ceiling light in the living room. Assuming the switch for the room was to one of the outlets for a lamp. After testing to find which outlet it was, to my surprise, it was all of the outlets in the room. Yes, One switch turns ON/OFF every outlet in my living room. All the outlets have 2 live, 2 neutral, 1 ground. The light switch has 2 wires going to it and the ground running from the romex directly out of the receptacle box. How do I have the outlets run continuously?
 
TL;DR
Multiple outlets wired to one switch. How do I remove switch from circuit
Recently moved into a house from the 70s. There's no ceiling light in the living room. Assuming the switch for the room was to one of the outlets for a lamp. After testing to find which outlet it was, to my surprise, it was all of the outlets in the room. Yes, One switch turns ON/OFF every outlet in my living room. All the outlets have 2 live, 2 neutral, 1 ground. The light switch has 2 wires going to it and the ground running from the romex directly out of the receptacle box. How do I have the outlets run continuously?
The best and easiest way to do it would be turn off the power and take the light switch out and splice the 2 wires on the switch together. Your switch will no longer work and the receptacles will have constant power. Please be careful and make sure the power is off.
 

Reply to remove switch from multiple outlets in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

Hi, I’m looking to install 3 meross smart switches for 3 lights: entrance switch: only 1 gang but 3 way switch bedroom switch: 2 gang (1 is 1...
Replies
9
Views
363
Hi, I installed 6 recessed lights in my living room. I’m now up to the wiring part of the project. There is an outlet in the room that is...
Replies
1
Views
466
Hello everyone... There are a total of 4 cables entering the junction box at the top of the staircase. Two 12/2 cables are coming in through the...
Replies
1
Views
439
DYI guy here with some basic knowledge of electrical craft. I am helping a buddy in his remodeled bathroom. His GFCI outlet was powered off vanity...
Replies
11
Views
969
Our family room is part of an addition built a few years ago. We had an issue with nuisance tripping on an AFCI and the electrician came and...
Replies
2
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock