Discuss Removing socket for overhead light fixture (Norway) in the Lighting Forum area at ElectriciansForums.net

neuvilla

DIY
Reaction score
3
This is a rather basic question, so please accept my apologies. I couldn't find the right search term, and I thought my situation was a bit unique as I live in Norway. And thank you so much for any advice you can give to me, it's really appreciated.

In Norway, its quite common to have sockets at the top of the wall to plug ceiling lights into. However, I would like to wire a light fixture directly into the house mains electric circuit, rather than to have it plug into the socket. Photo and video are in the link below to show you what I'm dealing with.

https://Upload the image directly to the thread.com/a/E1zH8rC

First, can I just remove the socket and put in some sort of junction box in place of it? Then I can use that to connect the wires from the switch and the wires from the light fixture. I've said junction box, but is this the right name for what I need?

Second, what is best practice for the earth wire, as the light fixture doesn't need/have an earth.

Third, when doing all of this, do I need to switch off the relevant circuit at the circuit breaker, or can I just ensure the light switch is in the off position.

Thank you so much for any help you can give.

P.S. It is also common, or at least was in the past, in Norway to have unconcealed wires!
 
This is a rather basic question, so please accept my apologies. I couldn't find the right search term, and I thought my situation was a bit unique as I live in Norway. And thank you so much for any advice you can give to me, it's really appreciated.

In Norway, its quite common to have sockets at the top of the wall to plug ceiling lights into. However, I would like to wire a light fixture directly into the house mains electric circuit, rather than to have it plug into the socket. Photo and video are in the link below to show you what I'm dealing with.

https://Upload the image directly to the thread.com/a/E1zH8rC

First, can I just remove the socket and put in some sort of junction box in place of it? Then I can use that to connect the wires from the switch and the wires from the light fixture. I've said junction box, but is this the right name for what I need?

Second, what is best practice for the earth wire, as the light fixture doesn't need/have an earth.

Third, when doing all of this, do I need to switch off the relevant circuit at the circuit breaker, or can I just ensure the light switch is in the off position.

Thank you so much for any help you can give.

P.S. It is also common, or at least was in the past, in Norway to have unconcealed wires!
2 - T8A3y89.jpg
Thanks for your help. I'm usually much better at IT than this! Anyway, in post below (waiting to be approved by moderators) there should be a video and photo.
 
Last edited:
The link you have included doesn't seem to be a valid URL, at least not for me!
Can you use the "Attach files" button ?
(Or maybe that's not available to you as a new member??)
 
This is a rather basic question, so please accept my apologies. I couldn't find the right search term, and I thought my situation was a bit unique as I live in Norway. And thank you so much for any advice you can give to me, it's really appreciated.

In Norway, its quite common to have sockets at the top of the wall to plug ceiling lights into. However, I would like to wire a light fixture directly into the house mains electric circuit, rather than to have it plug into the socket. Photo and video are in the link below to show you what I'm dealing with.

https://Upload the image directly to the thread.com/a/E1zH8rC

First, can I just remove the socket and put in some sort of junction box in place of it? Then I can use that to connect the wires from the switch and the wires from the light fixture. I've said junction box, but is this the right name for what I need?

Second, what is best practice for the earth wire, as the light fixture doesn't need/have an earth.

Third, when doing all of this, do I need to switch off the relevant circuit at the circuit breaker, or can I just ensure the light switch is in the off position.

Thank you so much for any help you can give.

P.S. It is also common, or at least was in the past, in Norway to have unconcealed wires!
 

Attachments

  • VID_20220801_161148.mp4
    6.7 MB
  • IMG_20220801_161219.jpg
    130.8 KB · Views: 3
This is a rather basic question, so please accept my apologies. I couldn't find the right search term, and I thought my situation was a bit unique as I live in Norway. And thank you so much for any advice you can give to me, it's really appreciated.
No need to apologise. Members of this forum are not supposed to give "step by step" instructions, really to preserve safety, but are always happy to help with general advice
In Norway, its quite common to have sockets at the top of the wall to plug ceiling lights into. However, I would like to wire a light fixture directly into the house mains electric circuit, rather than to have it plug into the socket. Photo and video are in the link below to show you what I'm dealing with.
thank you for posting those
First, can I just remove the socket and put in some sort of junction box in place of it? Then I can use that to connect the wires from the switch and the wires from the light fixture. I've said junction box, but is this the right name for what I need?
If this was the UK, one would probably use a 'Fused Connection unit' which is a switch and a fuse combined. The purpose to fuse down the connection to the capacity of the flex to the light, which is generally less than the fixed wiring capacity. And a switch to be able to isolate the supply to maintain the lamp.

However, with the caveat that I don't know your regulations, since it appears the flex on your lamp is similar to the size of the house wiring, and looking at the rest of your installation, it doesn't seem it will be made less safe by doing what you suggest. Indeed, since you are already running it via a socket apparently ready to fall off the wall, it would improve safety to make that a permanent connection.
Could you however tell us the rating of the fuse protecting that circuit?
Second, what is best practice for the earth wire, as the light fixture doesn't need/have an earth.
In the UK it's required to run the earth to the fixture, and in this situation leave it disconnected (safely isolated), so that if someone changes the light in the future, the earth is available. To me that metal light fitting looks a good candidate to have an earth connction, but if it has a box-in-a-box symbol on it (double insulated) you don't need to.
Third, when doing all of this, do I need to switch off the relevant circuit at the circuit breaker, or can I just ensure the light switch is in the off position.
You must switch it of at the mains circuit breaker. An electrician would then 'dead test' the circuit to make absolutely sure it was not live.
P.S. It is also common, or at least was in the past, in Norway to have unconcealed wires!
Also quite common in older houses in the UK
 
Last edited:
No need to apologise. Members of this forum are not supposed to give "step by step" instructions, really to preserve safety, but are always happy to help with general advice
Thank you.
thank you for posting those

If this was the UK, one would probably use a 'Fused Connection unit' which is a switch and a fuse combined. The purpose to fuse down the connection to the capacity of the flex to the light, which is generally less than the fixed wiring capacity. And a switch to be able to isolate the supply to maintain the lamp.

However, with the caveat that I don't know your regulations, since it appears the flex on your lamp is similar to the size of the house wiring, and looking at the rest of your installation, it doesn't seem it will be made less safe by doing what you suggest. Indeed, since you are already running it via a socket apparently ready to fall off the wall, it would improve safety to make that a permanent connection.
Could you however tell us the rating of the fuse protecting that circuit?
The fuse (a dii, bottle type) is 10 amps on this particular circuit.

In the UK it's required to run the earth to the fixture, and in this situation leave it disconnected (safely isolated), so that if someone changes the light in the future, the earth is available. To me that metal light fitting looks a good candidate to have an earth connction, but if it has a box-in-a-box symbol on it (double insulated) you don't need to.
I forgot to mention that we're putting in a new light fixture, a new Ikea one, which I assume will be double insulated (but will check).

So, if I understand correctly, with this new light fixture, I could replace the socket with a 'junction box'? Then, I'd run the circuit wires into that, isolate the earth inside the junction box, and then run some new cable from that junction box to the new Ikea light fixture?
You must switch it of at the mains circuit breaker. An electrician would then 'dead test' the circuit to make absolutely sure it was not live.
Thank you. Noted, and will do that.
Also quite common in older houses in the UK
 
The fuse (a dii, bottle type) is 10 amps on this particular circuit.
In that case, use the same gauge wire as the house wiring to connect between the 'junction box' and your new light.
So, if I understand correctly, with this new light fixture, I could replace the socket with a 'junction box'?
subject to above
Then, I'd run the circuit wires into that, isolate the earth inside the junction box, and then run some new cable from that junction box to the new Ikea light fixture?
Ideally you would continue the earth in the new cable from the junction box to the new light fixture, and isolate it there if not required!
 
In that case, use the same gauge wire as the house wiring to connect between the 'junction box' and your new light.

subject to above

Ideally you would continue the earth in the new cable from the junction box to the new light fixture, and isolate it there if not required!
Thank you so much for taking time out of your day to give me this general advice. It's really appreciated.
 

Reply to Removing socket for overhead light fixture (Norway) in the Lighting Forum area at ElectriciansForums.net

Similar Threads

I have 2 lights connected to 1 switch. I installed a led light fixture on one light, it had one red wire and one black wires. It was easy to match...
Replies
0
Views
293
I have installed a number of 120v smart light switches and smart bulbs which I have set up on a schedule via an app. I would like to add another...
Replies
1
Views
1K
My kitchen has track lighting. It consists of three halogen light bulbs. I've had the fixture for more than 25 years with no issues. Last night...
Replies
10
Views
908
I bought this house a couple months ago. It was built in 1952 (same as me) but has been rewired with yellow 12 awg Romex dated 2007. Looks like a...
Replies
7
Views
528
I am adding a light fixture in a room I am restoring in my 160 yo house. I have ran a new 12-2 w/ground wire from the ceiling box to a junction...
Replies
2
Views
881

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock