Discuss Renovated house low r2 readings ! in the UK Electrical Forum area at ElectriciansForums.net

Soulsurfer

-
Arms
Reaction score
143
Just been sorting out a right mess during a house renovation and tests on newly installed ring final are r1 0.35
rn 0.35 & r2 was expecting around 0.58 but had consistently 0.00 Ohms.
MFT was zeroed again from scratch and was still giving a zero resistance reading
Almost all cable is new and IR tests all perfect. Any ideas ? Thanks
 
Sounds like the earth has shorted on the beginning run of the cable as you had 0.35 on rn/r1 must be the earth ring is so short it reads 0.00 does your tester go to three figures? Have you tested at the middle socket? r2? end to end that would indicate if that was the case.
 
Back there Friday to finish up so I'll check more extensively then, closest socket to board 0.09 ohms which is very close to the board. Is a really small ring too. Cheers
Tested R1 +R2, and R1 to RN too etc to check all. Yes tester goes to 3 figures is Fluke 1653B
 
What position are you testing the ring from the consumer unit or socket ? I have had it in the past where had small ring and the dampness of plaster damp wall between the metal k.o. boxes have given a lower continuity reading than I should of had but not that low.
 
What position are you testing the ring from the consumer unit or socket ? I have had it in the past where had small ring and the dampness of plaster damp wall between the metal k.o. boxes have given a lower continuity reading than I should of had but not that low.
Tested at each socket on newly rewired small ring, as said expected around 0.58 and got 0.00! After 0.35 each on L's & N's cross connected.
 
Maybe cables have been jointed somewhere but cpcs have been connected together in one connection rather than connected in 2 separate connections.
But 0.00 ohms suggests that the cpc ends are crossed in the db with another circuit
 

Reply to Renovated house low r2 readings ! in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
2K
Slightly strange one this, replaced a few socket fronts in a dining room today, all wiring original but new plasterboard on a studded wall. Its a...
Replies
4
Views
1K
Hi everyone. Hopefully someone can help with a little mystery i had today. The issue is fixed but I want to understand what was going on to help...
Replies
8
Views
644
Hi All, Had a weird one this morning during an EICR. Testing a ring final circuit in a 2 bed flat… kitchen was on a separate ring. With only the...
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock