I'm about to change 40 x MR16/G5.3 fittings, do away with transformers and replace with mains GU10 Lamp holders double insulated and GU10 LEDs. I hoped to keep the existing Lamp fittings but was concerned as label states G5.3 12v 50w max.Is it safe to use GU10 LED in these fittings?IMG_8908.jpeg
 
No, it will not be safe to use them. They are not designed for 230V. As an aside they are also not fire rated so should not be fitted if any living quarters above unless you put a fire hood on them. New ones are not expensive and would be the safe and correct option.
In addition you would need to get an electrician to test the existing earth and also for him/her to check if the existing circuit is RCD protected and if so to test the RCD is within parameters (amongst other required tests).
 
Thanks for the replies, appreciate it. My initial idea was to replace Mr16 transformers with gu10 lamp holder as illustrated in photo, I had read that the double insulated GU10 holders don't require an earth? I thought this would be ok to use with existing MR16 lamp fittings but looks like I'm wrong.The MR16s were installed around 18 years ago by an electrician, the circuits are RCD protected. I thought replacing these with GU10s is something I could do myself, with some advice from you guys. So the Jcc twist and Lock might be the way to go then? any install advice, links etc greatly appreciated trying to keep cost to a minimum! light.jpg
 
option 3 is the best bet, or:
option 4: integrated fitting (like JCC V50, or similar).
 

Reply to Replace MR16 with GU10 LED - Help with Lamp fitting?? in the Lighting Forum area at ElectriciansForums.net

Similar Threads

Hi all, Great forum with lots of advice read and greatly received over the years! I have a question here that I am hopeful somebody here can...
Replies
16
Views
1K
Good Morning, I've used this forum for advice many times but this is my first time posting so I hope that this community can help! We're...
Replies
5
Views
1K
Hi there, I'm a competent DIYer that has done lots of with lighting over the years but have just moved into a house packed full of mr16 halogens...
Replies
15
Views
9K
Hi, I have to replace bath and shower downlights to IP rated. I thought they were GU10 so bought the GU10 fitment and bulbs. I fitted it and it...
Replies
7
Views
2K
I have 60+ of these Aurora down lights in 12v MR16 format and want to convert them to 230V GU10 LED by changing the lamp holder for something like...
Replies
9
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock