Discuss Replacement shower in the UK Electrical Forum area at ElectriciansForums.net
No they don't.If the manufactures instructions state to be rcd protected it does not matter what bs7671 says it must be rcd protected. They supersede bs7671
That relates to the process of erection, i.e. how high up the wall, the distance from windows or doors etc.134.1.1
Good workmanship ... Electrical equipment shall be installed in accordance with the instructions provided by the manufacturer of the equipment.
Could I suggest that you find a set of instructions where it is states that an RCD must installed?Had this with niceic before. Manufacturers instruction supersede 7671 . No more to be said. If you do not install to manufactures instructions it will not comply as they will never instruct you to do anything against the regs but they may ask you to go over and above the minimum standard.
as has been said...check manufactures instructions....
i personaly would RCD it but...
Had this with niceic before. Manufacturers instruction supersede 7671 . No more to be said. If you do not install to manufactures instructions it will not comply as they will never instruct you to do anything against the regs but they may ask you to go over and above the minimum standard.
I assume if manufacturers instructions supersede BS7671 then this would have to be listed as a departure from the regs on any certificate
This could also be interesting in a court if the manufacturers instructions due to errors did not fully meet the requirements of the regs and an incident occurred
That's my point spin. Your arguing against yourself. I said yes you said noInstructions for Triton:
The following notes are for guidance only:
5.1 A 30mA residual current device (RCD) must
be installed in all UK electric and pumped
shower circuits. This may be part of the
consumer unit or a separate unit.
Instructions for Gainsborough:IN THE INTERESTS OF ELECTRICAL SAFETY, A 30mA RESIDUAL CURRENT DEVICE (RCD) SHOULD BE INSTALLED IN ALL
UK 230-240V ELECTRIC SHOWERS. THIS MAY BE PART OF A CONSUMER UNIT OR A SEPARATE UNIT.
Instructions for Mira:It is strongly recommended that a 30 mA Residual Current Device (RCD) is
included in the electrical circuit. This may be part of the consumer unit or a separate unit.
Instructions for Aqualisa:
IN THE INTERESTS OF ELECTRICAL SAFETY, A 30mA RESIDUAL CURRENTDEVICE (RCD) SHOULD BE INSTALLED IN ALL UK 230-240V ELECTRIC
SHOWERS AND PUMPED CIRCUITS. THIS MAY BE PART OF A CONSUMER
UNIT OR A SEPERATE UNIT.
Creda and MX don't mention anything about RCDs.
That's my point spin. Your arguing against yourself. I said yes you said noInstructions for Triton:
The following notes are for guidance only:
5.1 A 30mA residual current device (RCD) must
be installed in all UK electric and pumped
shower circuits. This may be part of the
consumer unit or a separate unit.
Instructions for Gainsborough:IN THE INTERESTS OF ELECTRICAL SAFETY, A 30mA RESIDUAL CURRENT DEVICE (RCD) SHOULD BE INSTALLED IN ALL
UK 230-240V ELECTRIC SHOWERS. THIS MAY BE PART OF A CONSUMER UNIT OR A SEPARATE UNIT.
Instructions for Mira:It is strongly recommended that a 30 mA Residual Current Device (RCD) is
included in the electrical circuit. This may be part of the consumer unit or a separate unit.
Instructions for Aqualisa:
IN THE INTERESTS OF ELECTRICAL SAFETY, A 30mA RESIDUAL CURRENTDEVICE (RCD) SHOULD BE INSTALLED IN ALL UK 230-240V ELECTRIC
SHOWERS AND PUMPED CIRCUITS. THIS MAY BE PART OF A CONSUMER
UNIT OR A SEPERATE UNIT.
Creda and MX don't mention anything about RCDs.
no probs onions:biggrin:Ha ha sparkless not you. Sorry glen I take it back. Humble pie.
That's my point your arguing against yourself spin. I said yes you said noInstructions for Triton:
The following notes are for guidance only:
5.1 A 30mA residual current device (RCD) must
be installed in all UK electric and pumped
shower circuits. This may be part of the
consumer unit or a separate unit.
Instructions for Gainsborough:IN THE INTERESTS OF ELECTRICAL SAFETY, A 30mA RESIDUAL CURRENT DEVICE (RCD) SHOULD BE INSTALLED IN ALL
UK 230-240V ELECTRIC SHOWERS. THIS MAY BE PART OF A CONSUMER UNIT OR A SEPARATE UNIT.
Instructions for Mira:It is strongly recommended that a 30 mA Residual Current Device (RCD) is
included in the electrical circuit. This may be part of the consumer unit or a separate unit.
Instructions for Aqualisa:
IN THE INTERESTS OF ELECTRICAL SAFETY, A 30mA RESIDUAL CURRENTDEVICE (RCD) SHOULD BE INSTALLED IN ALL UK 230-240V ELECTRIC
SHOWERS AND PUMPED CIRCUITS. THIS MAY BE PART OF A CONSUMER
UNIT OR A SEPERATE UNIT.
Creda and MX don't mention anything about RCDs.
Triton:
The following notes are for guidance only:
5.1 A 30mA residual current device (RCD) must
be installed in all UK electric and pumped
shower circuits. This may be part of the
consumer unit or a separate unit.
Gainsborough:
IN THE INTERESTS OF ELECTRICAL SAFETY, A 30mA RESIDUAL CURRENT DEVICE (RCD) SHOULD BE INSTALLED IN ALL
UK 230-240V ELECTRIC SHOWERS. THIS MAY BE PART OF A CONSUMER UNIT OR A SEPARATE UNIT.
Mira:
It is strongly recommended that a 30 mA Residual Current Device (RCD) is
included in the electrical circuit. This may be part of the consumer unit or a separate unit.
Aqualisa:
IN THE INTERESTS OF ELECTRICAL SAFETY, A 30mA RESIDUAL CURRENTDEVICE (RCD) SHOULD BE INSTALLED IN ALL UK 230-240V ELECTRIC
SHOWERS AND PUMPED CIRCUITS. THIS MAY BE PART OF A CONSUMER
UNIT OR A SEPERATE UNIT.
Creda and MX don't mention anything about RCDs whatsoever.
Who are these manufacturers' that state an RCD must be fitted in their instructions?
The OP is not installing a circuit.Regulation 701.411.3.3
In specific locations such as those containing a bath or shower there is a requirement to provide RCD protection on all circuits, including the lighting and shower circuits.
That regulation along with manufactures instructions is enough for me to interpret rcd protection is required
I was just quoting that along with the instructions as a pair. Stating that is enough for me to rcd protectThe OP is not installing a circuit.
He is replacing an item of equimpent.
As such there is no requirement for him to install RCD protection.
I was just quoting that along with the instructions as a pair. Stating that is enough for me to rcd protect
That is not the case at all.This conversation is what I believe is half the problem of what is belittling our trade, guys working to the minimum standard rather than the higher standard which I would expect from fully qualified electricians. If we all worked to a higher standard customers would expect to pay the price for a quality job but unfortunately there are people out there working to a minimum standard which people producing a quality SAFE job cannot compete with. It's all good until there is another accident then people will say, " I wish I put an rcd on that shower " too late. Just my opinion.
look, given the nature of what were dealing with here (shower) whether or not the maufacurers state that RCD protection is to be installed is neither here nor there....it surely would be prudent to put the damn thing on an RCD....its about using your own judgement as well....i mean what happened to that eh?I completely agree but I was just pointing out that if a light or shower or socket front etc need replacing where do you draw the line with regards to adding rcd in like for like, In the real world I do recommend rcd but I don't think they are the be all and end all I see them as a second to good earthing and correct selection of opd
They are mentioned in some manufacturers' instructions, but in those instances it's only as a recommendation that one be installed.and i find it highly unlikely that an RCD wouldn`t be mentioned within manufactures instructions anyway
and so common sense has to take precident here....cost has to come secondry to safety spin...They are mentioned in some manufacturers' instructions, but in those instances it's only as a recommendation that one be installed.
As can be seen from the quotes I posted in my earlier post.
and so common sense has to take precident here....cost has to come secondry to safety spin...