Discuss Resistance bewteen circuits in the Industrial Electricians' Talk area at ElectriciansForums.net

J

Jimmyb

I just wondered why i would get a reading of 1400 - 1800ohms between lives on 2 different circuits one being a new circuit installed about a month ago by an other spark, the only reason i check was two ring mains that had been put into one mcb by the last sparks and told the customer he need a new board fitting to allow for the extra circuit and he would come back but then never answered the phone since, hence i got the job of changing the board.

I cant remember ever testing between to live on circuit and wondered if i was missing something and there is a normal reason for this. I did check all over circuit and all >2000.

Many Thanks

Jimmy
 
You need to do full continuity tests on both RFCs, paying particular attention to polarity at each accessory, I think you find at least one accessory is reverse polarity L-N or L-E. Also somewhere on the RFCs you have an approximate 40W of load (lamp, fan, etc.) still connected in circuit.
 

Reply to Resistance bewteen circuits in the Industrial Electricians' Talk area at ElectriciansForums.net

Similar Threads

Hi, Just been scratching my head about this one and wonder if I've missed anything. A few weeks ago I installed a new circuit for a 3kw oven and...
Replies
6
Views
775
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
DIY query Have narrowed down the source of an occasional trip to one light circuit which is a varilight v-pro master dimmer slave set up. This...
Replies
0
Views
387
Strange on this, we are wiring an extension at the moment and I would like to 3 way the (currently 2 way) landing switch to the new bedroom so...
Replies
14
Views
589
A BG fused connection unit, with neon. A boiler. Fuse out. Spur switched off. I was checking polarity after a colleague had 2nd fixed it and...
Replies
7
Views
728

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock