Search the forum,

Discuss Rewire Questions in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
23
I've been to see a flat which needs a rewire. The flat is being completely renovated. I've just recently qualified, I have done rewires before during my apprenticeship and understand it, but it is the first time taking one on on my own, I feel pretty confident as it is all partition walls which makes it easier. I have a few questions I was hoping you could help with:

Q1. How do you guys decide whether to install an RCD or RCBO board?
Do you pick based on the client/budget? I know an RCBO has the advantage of not wiping out half the place. So does it come down to price?

Q2. Type A or AC RCD/RCBO? I was going towards type A, I want to know what you guys think?

Q3. I am going to install smoke/heat detectors but what are the requirements? Which rooms need it? The kitchen I will put a heat of course! A smoke in the utility room and hallway. But is it necessary in the bedroom? Can anyone point me in the right direction where to find the info?

Q4. Heights for sockets and switches? I know the 450mm and 1200mm applies to mainly new builds. what heights would you recommend?

Q5. Dimmable LED strips with drivers. Can anyone recommend any good ones? Will I be able to put them on the same gang switch as the kitchen ceiling lights? They will be going under the kitchen units to light up the worktop. I've never bought any myself to install.

Q6. Are there any dimmer switches/modules which can work as master and slaves? The rewire specifies a 2 way intermediate in the bedroom and a 2 way in the kitchen/lounge.

Q7. Last but not least, the most famous question! How do you quote for the job? It is in central london. I have put £60 per socket/spur/switch, £50 for light/smoke/ex fan/appliances(mirror), £80 per hob point, £150 a grid switch (THEY ARE A NIGHTMARE IN MY OPINION). Is this too low? Do you guys price per point or hourly/daily?

What else do I need to know? Any other information would be appreciated.
I know I have to notify building control, I will get the tester to deal with this.
I have bought the building regs book its on its way, anything specific to read in there?

THANKS FOR ANY ANSWERS, HAVE A COOKIE ?
 
Not sure what you mean by the notifiable bit. Get the tester to sort that.
Are you not doing the testing and notification Yourself? Really if your doing the works maybe you should do the testing.

Youve bought the regs book. That’s good, but there is a lot more to this than the regs book. It will not tell you how to wire a flat.

Q1 it’s up to you. Your call. There are a few threads on here regarding rcbo or rcd. Personal preference.

Q2 Identify what an A type or AC type is for? And fit appropriate for the circuits in question.

Q3 there are no legal requirements to fit heat or smoke alarms in domestic premises. There are issues with rental domestic in so far as the landlord has a duty of care to protect there tenants, but nothing written in law.

Q4 I would recommend the 450 and 1200. they are good heights. It’s the hieghts I used in my own property, but it’s up to you and your client.

Q5 &Q6 speak to your supplier.

Q7 I work out the cost of material then work out how many days it will take. £300 per day plus materials plus an extra 10%, but this varies depending on your needs and the local area.
 
If I recall, Building regs require the installation of smoke alarm in a domestic properties, during major renovations, an example of which is a rewire. In any case, it would be madness for the client not to chose so.

Aico provide a simple planning online service, I’d also recommend fitting one of their control switches.

If you require two way dimmer switches, I believe Zano do something quite good.
 
Q7. Last but not least, the most famous question! How do you quote for the job? It is in central london. I have put £60 per socket/spur/switch, £50 for light/smoke/ex fan/appliances(mirror), £80 per hob point, £150 a grid switch (THEY ARE A NIGHTMARE IN MY OPINION). Is this too low? Do you guys price per point or hourly/daily?

too cheap esp. for London. unless those prices are for labour & cable., not inc.materials.
 
I've been to see a flat which needs a rewire. The flat is being completely renovated. I've just recently qualified, I have done rewires before during my apprenticeship and understand it, but it is the first time taking one on on my own, I feel pretty confident as it is all partition walls which makes it easier. I have a few questions I was hoping you could help with:

Q1. How do you guys decide whether to install an RCD or RCBO board?
Do you pick based on the client/budget? I know an RCBO has the advantage of not wiping out half the place. So does it come down to price?
RCBO every time
Q2. Type A or AC RCD/RCBO? I was going towards type A, I want to know what you guys think?
Type A unless AC is appropriate
Q3. I am going to install moke/heat detectors but what are the requirements? Which rooms need it? The kitchen I will put a heat of course! A smoke in the utility room and hallway. But is it necessary in the bedroom? Can anyone point me in the right direction where to find the info?
Read BS5839-6
Q4. Heights for sockets and switches? I know the 450mm and 1200mm applies to mainly new builds. what heights would you recommend?
Yep, we would as its a rewire
Q5. Dimmable LED strips with drivers. Can anyone recommend any good ones? Will I be able to put them on the same gang switch as the kitchen ceiling lights? They will be going under the kitchen units to light up the worktop. I've never bought any myself to install.
Zano, Varilight, Quinetic etc
Q6. Are there any dimmer switches/modules which can work as master and slaves? The rewire specifies a 2 way intermediate in the bedroom and a 2 way in the kitchen/lounge.
As above
Q7. Last but not least, the most famous question! How do you quote for the job? It is in central london. I have put £60 per socket/spur/switch, £50 for light/smoke/ex fan/appliances(mirror), £80 per hob point, £150 a grid switch (THEY ARE A NIGHTMARE IN MY OPINION). Is this too low? Do you guys price per point or hourly/daily?
I'd say your prices for central london are far too cheap
What else do I need to know? Any other information would be appreciated.
I know I have to notify building control, I will get the tester to deal with this.
I have bought the building regs book its on its way, anything specific to read in there?
What aren't you testing? If you have finished your apprenticeship you will have AM2/FICA etc so should be able to test?
THANKS FOR ANY ANSWERS, HAVE A CO
 
Not sure what you mean by the notifiable bit. Get the tester to sort that.
Are you not doing the testing and notification Yourself? Really if your doing the works maybe you should do the testing.

Youve bought the regs book. That’s good, but there is a lot more to this than the regs book. It will not tell you how to wire a flat.

Q1 it’s up to you. Your call. There are a few threads on here regarding rcbo or rcd. Personal preference.

Q2 Identify what an A type or AC type is for? And fit appropriate for the circuits in question.

Q3 there are no legal requirements to fit heat or smoke alarms in domestic premises. There are issues with rental domestic in so far as the landlord has a duty of care to protect there tenants, but nothing written in law.

Q4 I would recommend the 450 and 1200. they are good heights. It’s the hieghts I used in my own property, but it’s up to you and your client.

Q5 &Q6 speak to your supplier.

Q7 I work out the cost of material then work out how many days it will take. £300 per day plus materials plus an extra 10%, but this varies depending on your needs and the local area.
Hi, I am confident in the wiring of the flat there are just a few electrical items I am unsure about such as master/slave dimmers etc.

For the AC / A type I thought it would be necessary for most circuits as they will be rings, lights, oven, hob, boiler... pretty sure they all use some sort of DC internally?
 
Informative.
I knew about the carbon monoxide reg, but I didn’t know about the smoke on each floor.

however this is only in rented accommodation.

im pleased it exists, but concerned I didn’t know that one.

cheers
I have skimmed the link you have sent, I am assuming this only applies to rented properties?
The rewire is for someone who owns the property and is living there themselves. I will do more research.
 
If I recall, Building regs require the installation of smoke alarm in a domestic properties, during major renovations, an example of which is a rewire. In any case, it would be madness for the client not to chose so.

Aico provide a simple planning online service, I’d also recommend fitting one of their control switches.

If you require two way dimmer switches, I believe Zano do something quite good.
What do you mean by control switches?

I was opting for the standard aico optical smokes/heat and interconnect them.

I will check out Zano, this will be up to the client to provide. Do you know if they do modules only? otherwise they are stuck with their front plates only, like varilight multipoint, deta master/slave dimmers etc.
 
Q7. Last but not least, the most famous question! How do you quote for the job? It is in central london. I have put £60 per socket/spur/switch, £50 for light/smoke/ex fan/appliances(mirror), £80 per hob point, £150 a grid switch (THEY ARE A NIGHTMARE IN MY OPINION). Is this too low? Do you guys price per point or hourly/daily?

too cheap esp. for London. unless those prices are for labour & cable., not inc.materials.
This is only the labour prices. I will do the materials price separate then add the totals together. It is also a very close friend of mines girlfriend, having said that it is my first rewire and I'd like to get the job for experience/portfolio pictures. I am not a established business so I don't really have any crazy costs to cover.
 
sockets and switches, you fit them whare the customer wants them. while i agree with a 18" height for sockets, i hate light switches where a 3 year old can reach them. don't do new builds, so i always mount light switches at around chin height. sockets at knee height. who needs silly metric tape measures?
 
RCBO every time

Type A unless AC is appropriate

Read BS5839-6

Yep, we would as its a rewire

Zano, Varilight, Quinetic etc

As above

I'd say your prices for central london are far too cheap

What aren't you testing? If you have finished your apprenticeship you will have AM2/FICA etc so should be able to test?
I was thinking to go with Fusebox RCBO board with all type A.

Thanks I will check BS5839-6.

The heights are only for a new build house/flat though? pretty sure I read this somewhere, I will probably go with 450 & 1200 as it will be modern looking flat in london.

Also yes I have finished my apprenticeship/AM2. I will do the testing for my own satisfaction but some bits I am not too confident with. Also I am have not done my 2391, and I am not nic registered or any of those. So I will get a tester to certify it.
 
A new question arises:

When I went to see the place, the ceiling fan was wired, but the flexible ducting went up then into a flat pvc straight duct (approx 100x50mm) then went to somewhere where I could not see visually.

They said they will have a loft hatch in the bathroom as soon as you enter.

How would I go about deciding which fan to get?
I was thinking a centrifugal fan?
Was thinking about those inline fans too but you would need to climb into the loft space, and where the inline should be put, I don't think the ceiling will be too stable to work on...
 
Hi pppelec,
your confident but not to confident On some things.

do you know an electrician who can shadow you on this. Maybe pay the tester as you call him to go over the job at the beginning during and after. Also be there on hand or at the end of a phone.
it’s a great way of getting experience.
doing this without that back up may be too much first time.
I know that’s what I did when I did my first full rewire on my own.

the tester and certifyer will need to see the install at every stage anyway If he is taking liability for it.
 
What do you mean by control switches?

I was opting for the standard aico optical smokes/heat and interconnect them.

I will check out Zano, this will be up to the client to provide. Do you know if they do modules only? otherwise they are stuck with their front plates only, like varilight multipoint, deta master/slave dimmers etc.

Aico alarm control switch

Zano master/slave dimmers
 
Hi pppelec,
your confident but not to confident On some things.

do you know an electrician who can shadow you on this. Maybe pay the tester as you call him to go over the job at the beginning during and after. Also be there on hand or at the end of a phone.
it’s a great way of getting experience.
doing this without that back up may be too much first time.
I know that’s what I did when I did my first full rewire on my own.

the tester and certifyer will need to see the install at every stage anyway If he is taking liability for it.
In terms of wiring (first fix) I know I can do it 100%
Its just some of the components such as LED strips, dimmers.

I will be keeping in contact with the tester and documenting everything to him.
I will possibly get him to come look during and of course when he does the test.

Also I posted a question just above about a fan, any idea?

Thanks
 
In terms of wiring (first fix) I know I can do it 100%
Its just some of the components such as LED strips, dimmers.

I will be keeping in contact with the tester and documenting everything to him.
I will possibly get him to come look during and of course when he does the test.

Also I posted a question just above about a fan, any idea?

Thanks
Is your tester registered Third Party Certification?
 
I was thinking to go with Fusebox RCBO board with all type A.

Thanks I will check BS5839-6.

The heights are only for a new build house/flat though? pretty sure I read this somewhere, I will probably go with 450 & 1200 as it will be modern looking flat in london.

Also yes I have finished my apprenticeship/AM2. I will do the testing for my own satisfaction but some bits I am not too confident with. Also I am have not done my 2391, and I am not nic registered or any of those. So I will get a tester to certify it.
Fitted dozens of Fusebox CU's and they are fine.

Agree that the heights are for new builds but why not bring the installation up to modern standard when you have an opportunity to do so.

I dont understand how you will get somebody else to test and sign off your work?
 
I haven't fitted Type AC in years. As far as I'm concerned there is no great reason generally speaking to fit Type AC any more. Personally I wish they would just follow the rest of the world and ban them, and then everyone would be competing with the same spec.

On a recent EV installation I did unfortunately someone had decided to helpfully "leave it ready" including a single pole Type AC RCBO and a cracked cooker switch (with loose terminals) as an isolator. Once I had finished the job (including a double pole Type A RCBO and a rotary isolator) the other electrical worker arrived and had a go at me and got all defensive as to why I had ripped his RCBO out and replaced it. No amount of explanation that it needed to be Type A at a minimum, and also needed to interrupt all live conductors and not merely the phase conductor seemed to satisfy him.

He had also put 16mm^2 tails through a 40mm knockout in the DB with a bit of grommet strip round it doing wonders for the IP ratings, and popped a load of knockouts at the bottom ungrommeted for the cable entries, and even a spare 32mm knockout on the side not being used. There was honestly more work correcting what he had done than had he left the bloody thing alone for me to do it in the first place.
 
I could never work out how an AC type would be more suitable than an A, I think it all used to be down to cost, but this has largely been eroded in recent times.

And a bit controversial why they are still available as single pole. (tin hat)
 
Fitted dozens of Fusebox CU's and they are fine.

Agree that the heights are for new builds but why not bring the installation up to modern standard when you have an opportunity to do so.

I dont understand how you will get somebody else to test and sign off your work?
Initial verification...?

Me as the designer and constructor, him as the tester?
 
I was thinking to go with Fusebox RCBO board with all type A.
For many that is the default sort of choice, as type AC RCD are going out almost certainly with revised regs and the cost of the Fusebox RCBO setup is not much more than a dual RCD board.

Also they have SPD (I think) as standard, if not make sure that is included. Some ask the client and get drawn in to arguments on the risk vs. cost but for the < £100 for one on practically any board it is hardly worth the time and effort to quote two figures and discuss/justify it.
 
A new question arises:

When I went to see the place, the ceiling fan was wired, but the flexible ducting went up then into a flat pvc straight duct (approx 100x50mm) then went to somewhere where I could not see visually.

They said they will have a loft hatch in the bathroom as soon as you enter.

How would I go about deciding which fan to get?
I was thinking a centrifugal fan?
Was thinking about those inline fans too but you would need to climb into the loft space, and where the inline should be put, I don't think the ceiling will be too stable to work on...
An online fan is a great option when you have a loft as you get the benefit of noise reduction too. Which is especially handy at night. Your issue will likely be the 4 " exit hole. Will it be roof, wall or possibly soffit. You need to check the easiest option. If it's too difficult for you to do yourself get the homeowner to arrange it
 
An online fan is a great option when you have a loft as you get the benefit of noise reduction too. Which is especially handy at night. Your issue will likely be the 4 " exit hole. Will it be roof, wall or possibly soffit. You need to check the easiest option. If it's too difficult for you to do yourself get the homeowner to arrange it
Should an inline be fitted in with a standard/timer axial fan or just a grill?
It is in a flat I am not sure where it goes out, if I take the job on, I will investigate when doing the downlights.
 
Should an inline be fitted in with a standard/timer axial fan or just a grill?
It is in a flat I am not sure where it goes out, if I take the job on, I will investigate when doing the downlights.
Timer on the fan is the homeowners call. I usually wire the fan direct to the light switch rather than loop it from bathroom light. If homeowner wants fan switched separately he then has that option.
 
Timer on the fan is the homeowners call. I usually wire the fan direct to the light switch rather than loop it from bathroom light. If homeowner wants fan switched separately he then has that option.
sorry let me rephrase, what I meant was... If I install the inline fan in the loft space like you recommend because of of the noise, am I meant to install the inline fan motor with an axial fan or just the inline fan on its own with a grill? I would of thought it would be better with an axial fan as the axial fan pushes to the inline, then the inline helps push it out more...
yes I agree with the separate switching, I have that at home
 
sorry let me rephrase, what I meant was... If I install the inline fan in the loft space like you recommend because of of the noise, am I meant to install the inline fan motor with an axial fan or just the inline fan on its own with a grill? I would of thought it would be better with an axial fan as the axial fan pushes to the inline, then the inline helps push it out more...
yes I agree with the separate switching, I have that at home
My modus operandi with inline fans has always been to buy the complete kit from the wholesalers.I always go for highest wattage. Nothing as pleasing as watching a sheet of toilet paper stuck to the grill when extractor fan operates. I normally connect fan with flex first and check its operation before installing it in the attic. If fan has a timer I make sure homeowner decides the overrun time before I install it. It can be a nuisance mucking about with a fan timer in a small attic. Lastly a little rubber placed between the fan and the wooden grounds it's mounted to reduces vibration and noise.
 
My modus operandi with inline fans has always been to buy the complete kit from the wholesalers.I always go for highest wattage. Nothing as pleasing as watching a sheet of toilet paper stuck to the grill when extractor fan operates. I normally connect fan with flex first and check its operation before installing it in the attic. If fan has a timer I make sure homeowner decides the overrun time before I install it. It can be a nuisance mucking about with a fan timer in a small attic. Lastly a little rubber placed between the fan and the wooden grounds it's mounted to reduces vibration and noise.
soooo do you use the inline fan with just a grill mounted in the ceiling of the bathroom then? you don't use the inline + ordinary extractor fan? could you link me the kit pleaseeee
 
soooo do you use the inline fan with just a grill mounted in the ceiling of the bathroom then? you don't use the inline + ordinary extractor fan? could you link me the kit pleaseeee
Apologies. Misunderstood your question. Your phrase "inline + ordinary extractor fan" is unfamiliar to me. An inline fan by definition is "in the line" of air extraction with a flexi connected to the ceiling grill in the bathroom and a flexi connected to the wall or roof outlet. An ordinary extractor fan has a flexi on one end only. Don't have any links to hand but it's a standard item in any wholesalers
 
Apologies. Misunderstood your question. Your phrase "inline + ordinary extractor fan" is unfamiliar to me. An inline fan by definition is "in the line" of air extraction with a flexi connected to the ceiling grill in the bathroom and a flexi connected to the wall or roof outlet. An ordinary extractor fan has a flexi on one end only. Don't have any links to hand but it's a standard item in any wholesalers
so from the grill, how far into the flexi ducting do you install the in line fan? would you recommend straight duct over flexi duct if it is possible? because of the air flow resistance when hitting the grooves of the flexi duct?
 
Its not the airflow resistance on flexible ducting I find that is the problem, but the condensation that occurs on the grooves if extracting from a bathroom or kitchen, condensation trap and drain needed, if possible I try to always use solid duct, not popular as its more difficult to fit and takes time, any inline fan I also suspend from the rafters in a loft installation as this cuts down the noise considerably.
 
Its not the airflow resistance on flexible ducting I find that is the problem, but the condensation that occurs on the grooves if extracting from a bathroom or kitchen, condensation trap and drain needed, if possible I try to always use solid duct, not popular as its more difficult to fit and takes time, any inline fan I also suspend from the rafters in a loft installation as this cuts down the noise considerably.
There is no rafters, this is a flat with a concrete ceiling above the plasterboard. Would you say to suspend it from the concrete ceiling then? Can I not put it in a big enclosure to trap the noise? Suspending seems like a lot of work
 
so from the grill, how far into the flexi ducting do you install the in line fan? would you recommend straight duct over flexi duct if it is possible? because of the air flow resistance when hitting the grooves of the flexi duct?
Straight duct is always preferable but circumstances may limit its use. Your exit hole location (roof, wall or soffit) and your extract fan location will determine what you use. You will want to keep your duct run as short as circumstances allow. From the grill I normally mount the fan approx 2 to 3 feet away using flexi.If the exit is through the roof then I use another section of flexi. If the exit is through the soffit (or wall) it's usually a longer run and here is where straight duct is useful to provide a nice sloping flow to the exit hole with the final foot again in flexi
 
Straight duct is always preferable but circumstances may limit its use. Your exit hole location (roof, wall or soffit) and your extract fan location will determine what you use. You will want to keep your duct run as short as circumstances allow. From the grill I normally mount the fan approx 2 to 3 feet away using flexi.If the exit is through the roof then I use another section of flexi. If the exit is through the soffit (or wall) it's usually a longer run and here is where straight duct is useful to provide a nice sloping flow to the exit hole with the final foot again in flexi
Okay got you! its possible for me to use a straight duct as the rest continuation of the flat pvc duct is above the existing fan location. When doing a 90 degree bend into the duct would you recommend putting 2 x 45 degrees together then for the swooping like you said?
 
Straight duct is always preferable but circumstances may limit its use. Your exit hole location (roof, wall or soffit) and your extract fan location will determine what you use. You will want to keep your duct run as short as circumstances allow. From the grill I normally mount the fan approx 2 to 3 feet away using flexi.If the exit is through the roof then I use another section of flexi. If the exit is through the soffit (or wall) it's usually a longer run and here is where straight duct is useful to provide a nice sloping flow to the exit hole with the final foot again in flexi
Or Lord mount it straight onto an external wall.
Do you install a 3amp fuse inline of your extractor fans? they show on the installation instructions to do it...
 

Reply to Rewire Questions in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Looking for some advice and timescale here. I'm not an electrician just a tennet with a housing association. I've been offered top floor flat in a...
Replies
6
Views
521
I have been asked to change cu from old fuse board which has 6 fuses. Only 4 fuses are used. The first fuse feeds cooker circuit. This is not used...
Replies
17
Views
902
I've asked a similar question before I think and we came to the conclusion that apart from new houses and HMO's etc there aren't any rules about...
Replies
3
Views
371
Hi I have a job where customer has two families one families lives upstairs and one family will live downstairs. As the property is going through...
Replies
12
Views
806
In a property with two consumer units one for the ring main etc., and the other for the 1970s storage heaters (storage heater CU looks like it’s...
Replies
14
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top