mickytuff

Hi all had a weird one today, actually make it two, tested ringfinal continuity at the board lives were 0.00 and so were neutrals, earths were the same too, not sure why, is it a ring that has been interconnected causing a duff reading??
Secondingly tested another property's ringfinal circuit and got 30 ohms, very high- across lives an neutrals, earths were 49 ohms.........has anybody discovered similiar readings as i need to put an observation against these results and i would be even happier if i knew what they suggested/what was wrong with these circuits?? :sad_smile:
 
Hi all had a weird one today, actually make it two, tested ringfinal continuity at the board lives were 0.00 and so were neutrals, earths were the same too, not sure why, is it a ring that has been interconnected causing a duff reading??
Still wouldn't be 0.00.
Did you still have the meter nulled on wander lead?

Secondingly tested another property's ringfinal circuit and got 30 ohms, very high- across lives an neutrals, earths were 49 ohms.........
Odd that the proportions are right - just 100 times to high. Still thinking.
 
[B said:
mickytuff;666796]Hi all had a weird one today, actually make it two, tested ringfinal continuity at the board lives were 0.00 and so were neutrals, earths were the same too, not sure why, is it a ring that has been interconnected causing a duff reading??
[/B]Secondingly tested another property's ringfinal circuit and got 30 ohms, very high- across lives an neutrals, earths were 49 ohms.........has anybody discovered similiar readings as i need to put an observation against these results and i would be even happier if i knew what they suggested/what was wrong with these circuits?? :sad_smile:

Superconductivity !!
 
Might be worth checking your testers leads mate, had the same problem before even when nulled readings jump about because a dodgy connection.

- - - Updated - - -

Not sure what happened to the grammar then!
 
Hi all had a weird one today, actually make it two, tested ringfinal continuity at the board lives were 0.00 and so were neutrals, earths were the same too, not sure why, is it a ring that has been interconnected causing a duff reading??
Secondingly tested another property's ringfinal circuit and got 30 ohms, very high- across lives an neutrals, earths were 49 ohms.........has anybody discovered similiar readings as i need to put an observation against these results and i would be even happier if i knew what they suggested/what was wrong with these circuits?? :sad_smile:

Joking aside... what you are describing is not possible ( zero ohms ) Unless you forgot to seperate the legs at the CU !
 
My testers fine, batteries fully charged, and checked readings on my spare meter, exactly the same so the readings are correct, i think the ring is interconnected very close to the board and is duffing the reading up hence the 0.00 which is obviously not a correct/compliant reading as it suggests no resistance............there must be a reason for it
 
...ahhh uve replied whilst i replied, if its doing it on several meters then its obviouslly not going to be them. Sometimes you can null though and immediatley after its still not nulled. There will be a simple explanation.
 
hes in swiss alps, sern ..... you cant be getting zero... dont null leads and see what they read..., maybe incorrect seting or or or oor orrrrrrrrr
 
so no explanation then oh well worth a try, it must b a freak of electric nature, or more likely a duff ring, either way code 2 requires further investigation to locate and then rectify........
 
My testers fine, batteries fully charged, and checked readings on my spare meter, exactly the same so the readings are correct, i think the ring is interconnected very close to the board and is duffing the reading up hence the 0.00 which is obviously not a correct/compliant reading as it suggests no resistance............there must be a reason for it

Ok if you think the ring is interconnected close to the board why did you not open a socket at the half way point and test there. I would suspect ring leaving board probably straight to a JB then on to sockets.
 
Seen readings like this once - the CU had been moved down the wall and the offending JB was under the floor board - the sparky had connected 4 cables into one 30A jb!
 

Reply to Ring final continuity readings............. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi guys. Having a weird problem in a house that has suddenly happened. One half of the ring main has 240ish volts (fluctuates of course), and...
Replies
9
Views
513
Hi so i am doing a test on sockets on a ring Final circuit for family member. Got my end to ends r1 0.62, rn 0.64, r2 0.97, identified opposite...
Replies
3
Views
2K
Hello, I'm not an electrician, more one of those 'competent DIYers', so probably the worst kind :) My electric shower broke, the shower firm came...
Replies
13
Views
1K
Hi, I would love some help understanding an issue I’m having on a 16mm SWA cable running from the CU in my house to the CU in the shed. I believe...
Replies
15
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock