I did remove a couple of other cables of similar size to see if that was the case but ran out of time, will try again tomorrow. Wasn't overly bothered as all other tests were fineMixed up the wires?
I did remove a couple of other cables of similar size to see if that was the case but ran out of time, will try again tomorrow. Wasn't overly bothered as all other tests were fine
Is this a twin and cpc installation? have you managed to identify the individual cables? if yes then it's probably a loose or missing connection at one of the sockets, or a bad connection during testing.Testing my extensions wiring today and noticed cpc fails continuity. Howevery I have continuity from outward leg to main earthing bar in CU
Any ideas how ?
I did remove a couple of other cables of similar size to see if that was the case but ran out of time, will try again tomorrow. Wasn't overly bothered as all other tests were fine
Agree and some thanks for the help, not holding my breath though.Nice of him to get back on and let us know how he did!
You would have thought so.^^
I still don't understand. End to end continuity tests are the first to do on a new or a modified ring circuit.
Surely you know which are the correct ends?
AhhhhAh, must have miss led you some what, I didn't complete the wiring in my extension just testing after adding a couple of points in the kitchen.
Ah, must have miss led you some what, I didn't complete the wiring in my extension just testing after adding a couple of points in the kitchen.
Seems you're not the only one to get his wires crossed, eh?Easy girls been busy, resolved by trying all the other CPC's on the board. I knew it was there as i said before as i was getting continuity between CPC and board