They could all be spurs from the two sockets at the other side of the room??!!
Just a thought.
Jay
Just a thought.
Jay
Discuss Ring main Figure of 8..... in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
The op stated he installed the circuit so he should know how it is wired
Yes sintra all tests were carried out correctly and I'm sure it was wired in 1 loop! I will test again tomorrow the meter was jumping in readings sporadically so could be that. Haha Jay that would make the most sense!
Make sure your batteries in your tester are not on there way out my resistance readings always start playing up when they need changing !!
Sometimes the leads from your MFT can give dodgy readings. Try using croc clips on the actual cables of the actual sockets. If you hold them tight, they will give a better, more accurate reading. At least this would tell you if it was the sockets themselves!
Jay.