Discuss Running 2 phase in swa in the UK Electrical Forum area at ElectriciansForums.net

The supply is 2 phase from cut out fuses to meter, and meter to isolator. From isolator to DB is 4 core 35mm. 415v between phases.
If it's a 2 phase supply, the voltage between phases is 460 volts (480 in old money).
The implication from the OP is that he has two out of three lines of a 3-phase supply, hence the 400 / 415V between phases. This is not unheard of in areas that have 3-phase 4-wire street mains but 3-core service cables from the 3-wire DC days. We have it in our street; two lines, two cutouts and at one time, two meters, because when the area changed over to AC the distributors were relaid in 4-core but the service cables were not.

This is why I prefer to call 230-0-230 (460) by the name 'split phase' instead of two-phase, to avoid the ambiguity. What the OP appears to have, and what I have in my house, I call 'two-out-of-three phase' to indicate that they are 120° apart and there is a third phase in the supply network that is not present at the origin.

IMO and strictly speaking, 2-phase means a system where the phases are 90° apart, which was used in the early days of polyphase AC instead of 3-phase. Both systems offered a rotating field vector so induction motors were self-starting and had no torque-zeroes, but 3-phase was more economical of copper and became the preferred system. I believe that Croydon still has some 2-phase 90° distributors serving single-phase customers, using the old triple-concentric cables. They are fed from Scott-connected transformers in the substations to spread the load across a 3-phase HV supply.

FWIW my very first post on this forum about 15 years ago was on these definitions. Someone was saying that a single-phase welder with a 400V input was '2-phase' when what they meant was that it connected between two lines of a 3-phase supply to get the 400V and confusion reigned.
 
The implication from the OP is that he has two out of three lines of a 3-phase supply, hence the 400 / 415V between phases. This is not unheard of in areas that have 3-phase 4-wire street mains but 3-core service cables from the 3-wire DC days. We have it in our street; two lines, two cutouts and at one time, two meters, because when the area changed over to AC the distributors were relaid in 4-core but the service cables were not.

This is why I prefer to call 230-0-230 (460) by the name 'split phase' instead of two-phase, to avoid the ambiguity. What the OP appears to have, and what I have in my house, I call 'two-out-of-three phase' to indicate that they are 120° apart and there is a third phase in the supply network that is not present at the origin.

IMO and strictly speaking, 2-phase means a system where the phases are 90° apart, which was used in the early days of polyphase AC instead of 3-phase. Both systems offered a rotating field vector so induction motors were self-starting and had no torque-zeroes, but 3-phase was more economical of copper and became the preferred system. I believe that Croydon still has some 2-phase 90° distributors serving single-phase customers, using the old triple-concentric cables. They are fed from Scott-connected transformers in the substations to spread the load across a 3-phase HV supply.

FWIW my very first post on this forum about 15 years ago was on these definitions. Someone was saying that a single-phase welder with a 400V input was '2-phase' when what they meant was that it connected between two lines of a 3-phase supply to get the 400V and confusion reigned.
What you said is what the property has, 2 out of 3 lines entering the property. As an installation electrician I've never came across this before, therefore apologies for the wrong terminology. So from now on it's best to call this a 2 line supply?
 
I'm just being pedantic, ignore me. Two phases out of a three phase supply. Or two-phase, no-one thinks about 'real' 2-phase any moreunless they work for the DNO in Croydon (if that's still in use).
 

Reply to Running 2 phase in swa in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have a scenario where there is a three phase DB in a commercial property where there are mixture of three phase and single phase washing...
Replies
2
Views
842
I am trying to understand 3 phase volt drop. I understand single phase VD. Lets say we have a 70 meter run of 35mm, 5 core cable from the supply...
Replies
6
Views
2K
When I joined this forum a decade or so back, there was a discussion going on about a welder that was connected with a 3-core cable to L1, L2 and...
Replies
3
Views
2K
So, the actual job is on a farm. I think I'll keep things simple at the moment and just ask about voltage drop. I'll come on to earthing and...
Replies
11
Views
2K
Been looking at a CU change in a small office and would appreciate comments on the following. Office is supplied from the mains intake in the...
Replies
52
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock