Discuss S plan not firing boiler for hot water in the Central Heating Systems area at ElectriciansForums.net

Reaction score
2
Hello all!

I'm a plumber and have a customer where the s plan is working fine for both zones (ground floor, 1st floor + cylinder) but not firing the boiler when hot water demand from the cylinder is operated. 2 port valve opens and pump runs but boiler shows no demand for heat. Any ideas why? Id be very grateful :)

When I turn programmer on for one of the heating zones the cylinder does begin to heat up...
 
The hot water valve is obviously opening if its being asked to by the programmer/cylinder thermostat if its heating up when one of the other zones is calling for heat. Seems a little strange the pump is working but not firing the boiler as the pump would either be connected to the pump live terminal in the boiler which means the boiler would have to be receiving a call for heat or connected to the oranges of the valves which only becomes live when the valve opens because it closes the switch between the grey and orange (grey being permanent live). Are you sure the pump is operating just on the hot water call?
 
need to start digging in the wiring centre with your voltage tester I think. check for voltage on the orange of the HW valve when its calling for heat with just HW turned on, on the programmer and the cylinder thermostat turned up.
 
need to start digging in the wiring centre with your voltage tester I think. check for voltage on the orange of the HW valve when its calling for heat with just HW turned on, on the programmer and the cylinder thermostat turned up.

I will do. So no voltage would suggest 2 port valve not communicating with wiring centre and message not getting back to the boiler?
 
I will do. So no voltage would suggest 2 port valve not communicating with wiring centre and message not getting back to the boiler?


Yeah if there is no voltage on the orange but there is voltage on both the brown and grey and the valve has opened it would suggest the micro switch in the valve head is shagged. If there is voltage on the orange check if there is voltage at the switched live terminal in the boiler if there is no voltage at this terminal it would suggest a shyte connection between the orange and the boiler switch live.
 
Yeah if there is no voltage on the orange but there is voltage on both the brown and grey and the valve has opened it would suggest the micro switch in the valve head is shagged. If there is voltage on the orange check if there is voltage at the switched live terminal in the boiler if there is no voltage at this terminal it would suggest a shyte connection between the orange and the boiler switch live.

You sir are a genius. I will try this and report back.
 

Reply to S plan not firing boiler for hot water in the Central Heating Systems area at ElectriciansForums.net

Similar Threads

I've always thought I was quite good a wiring heating systems, I can do Y plan, S plan, UFH set ups, "normal" thermal stores etc, you name it and...
Replies
4
Views
951
Hello, I hope you are well, I have fitted a few Nests but only to Combi, S and Y plan systems just been looking a job where I’m doing the kitchen...
Replies
9
Views
2K
I have a fully pumped Y plan heating system using a Potterton EP2 programmer. Drayton MA1 Diverter valve. I have just replaced the Actuator head...
Replies
4
Views
618
Hi my name is Gintas I connected solar hybrid inverter to my house ring supply and it work very well everything except the gas boiler for on...
Replies
3
Views
278
(Or that might be should a failed HW valve keep boiler running) Woke up this morning to find the boiler still running even though all timers off...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock