Discuss Safety - does switching off at consumer unit isolate the circuit switched? in the DIY Electrical Advice area at ElectriciansForums.net

Joric1

DIY
Reaction score
0
I am not an electrician (as you will see from the question!) and I am not planning on doing any electrical alterations. My question is one of safety. I wanted to move a couple of sockets on a kitchen ring main. So I switched off that circuit on the RCD board and all the sockets were then dead. I thought that this isolated the ring main and so was safe to work on? In the process of trying to move one of the sockets I had to take out the wiring and at this point the RCD for the whole downstairs tripped – I was alerted by the lights going off. I thought at first this was a coincidence and a separate fault had developed in the lights! But after turning everything back on except the socket circuit the same thing happened again just when I moved the wires around. My question is, would this be normal for what I thought was a dead circuit to trip the RCD switch? Is there some residual sensitivity to short circuits in a circuit that is switched off? Or when you switch the switch are you not really disconnecting? Is it safe to carry on messing about with the sockets? Is it safe if I switch off the RCD control switch for the downstairs? Or do I have to switch off at the mains? On the other hand is this an actual fault? Should I be calling an electrician? Should I call back the electrician who installed the consumer unit less than a year ago – could it be wired up incorrectly? I have never had any trouble with the sockets when connected, before or after. Please excuse ignorance.
 
Yes this is normal.

When you short N and E on the socket circuit, it provides an alternative path for a small amount of current from other circuits on that RCD, which will often trip the RCD.

It does not indicate anything wrong with the consumer unit install. In fact I'd be worried if it didn't trip (assuming there are other circuits in use at the time).
 
Last edited:
Rcd’s work in a way that if you touch the live or neutral, it will trip.
turning off a circuit breaker only disconnects the live.

what you possibly did was touch the neutral to the earth wire or earthed backbox, causing the rcd to trip, because it thinks there’s a fault.
 
Thank you both - replies greatly appreciated. I tried the experiment N to E and that indeed seems to be what did it. That means I can get on and move the sockets ready for tiling tomorrow, with confidence. Although... when you say "small amount of current" I'm assuming you mean not enough to feel it! :)
 
The small amount of current is anything up to 30mA. Stated on the Rcd. (Other ratings are possible, but unlikely in domestic)

Different story if you touched a 230v live cable. You would still receive a shock, but only for 40ms or less. Still long enough to feel it.

Both statements here are true, IF the RCD is working properly.
 

Reply to Safety - does switching off at consumer unit isolate the circuit switched? in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

Hi, The `power went out throughout the house this afternoon but only to the sockets, the lighting circuits are all fine. I went to the consumer...
Replies
9
Views
1K
HI My flat just failed the EICR because there is no RCD in the consumer unit. There is no space for a new RCD as the consumer unit is full. Do I...
Replies
18
Views
2K
I wondered if it is OK to have 2 x Main Switches in the same consumer unit. One feeding the RCBOs in the House and one feeding the CU in a garage...
Replies
16
Views
774
Hi there, Any advice on this would be greatly appreciated! (Note, this is not a DIY, I'm using a fully qualified electrician, just posting here...
Replies
8
Views
653
Hi I have a job where customer has two families one families lives upstairs and one family will live downstairs. As the property is going through...
Replies
12
Views
679

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock