Discuss Secondary consumer unit from SWA cable in the UK Electrical Forum area at ElectriciansForums.net

Others have already covered the main points. However, on the specifics of feeding the SWA cable you don't need or indeed want a 30mA RCD/RCBO at the supply point as it is just asking for spurious trips, and due to the earthed armour you are already protected from shock on a cable penetrating accident (e.g. nailing a buried section).

But how you protect the new sub-main against faults or overload depends on the characteristics of your incoming supply. If it is of adequately low Ze (fault impedance) then a fused-switch is you best choice and you do get metal bodied ones that the SWA cable can be directly glanded on to.

If you cannot meet an adequately low end of sub-main Zs to achieve fast enough disconnection times (5s for sub-main on TN earth, or 1s on TT earth) then you would need a RCD, but that could be a 100mA or 300mA delay type so you achieve selectivity with downstream RCD/RCBO in the garage CU and don't have everything going off on a single fault on a final circuit.

Finally if going with a switched-fuse you might want to consider your supply fuse (in the DNO cut-out) both for the above points about the total load you can safely draw, and also so you can chose the sub-main fuse to be selective with that so a major fault such on the garage circuit will not take out the home's supply and need a call to the DNO to replace the sealed fuse in their equipment. For BS88 series fuses that is usually achieved at a 1.6:1 ratio, so if your main supply is 100A then a 63A sub-main fuse should be totally selective with it, if your supply is 80A then a 50A sub-main, etc.

You could use a MCB to feed the sub-main but generally they have much poorer selectivity with downstream faults, and going for a high magnetic trip curve to help mitigate that normally results in a harder to meed end of cable Zs, compared to a similar rating of fuse.
 
May seem like a minor point, but please realise the difference between an EV charge point, and an EV charger.

An EVCP presents the supply "13A", 16A 32A etc, and uses the charger within the vehicle, so the charge is limited by the lower of the EVCP or vehicle itself (eg a vehicle with a 5kW charger internally could only charge at ~20A when on a 32A EVCP or 16A when on a 16A EVCP)

An EV charger is usually something like 50kW or 75kW plus and provides DC directly to the vehicle which bypasses the charger within the vehicle.
Thank you Julie. Shows my naivety. I thought the name was interchangeable. I do indeed mean an EVCP. The ones I have been looking at are 7.4kw 32 amps
 
Thank you Julie. Shows my naivety. I thought the name was interchangeable. I do indeed mean an EVCP. The ones I have been looking at are 7.4kw 32 amps

Most cars still have onboard chargers around 7kW, but PHEVs are usually around 3.3kW

There are newer vehicles with 11kW chargers onboard.
 
Make sure any plan fully considers the EVCP as this as it can affect several factors of this design.
I have a mini electric on order which won't arrive until Jan 2023 so I have a bit of time. if it has to be 13amp would be a shame but so be it
You certainly don't want a 13amp EVCP. (In my view these should really be banned!)
I'd be fairly certain there will be a way to fully utilise a 7Kw EVCP but you'll need your sparks help to arrive at this. There are solutions available for some charge points to wirelessly connect a current monitor.
 

Reply to Secondary consumer unit from SWA cable in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I am planning to go semi off grid with a victron and battery system. The system will be installed in an out building about 20 meters away from...
Replies
7
Views
792
Hi guys, I have supplied my Shed with a 6mm SWA cable into a nice consumer unit. In there I have a 6Amp MCB for the lights and a 16 A supplying a...
Replies
25
Views
1K
I wondered if it is OK to have 2 x Main Switches in the same consumer unit. One feeding the RCBOs in the House and one feeding the CU in a garage...
Replies
16
Views
864
Was having a poke around the old man's house today. Anyway. DB is under stairs (18th ed following a recent extension. Not done by me but it's...
Replies
7
Views
751
Hi everyone, A diversity question concerning 2 consumer units fed from 100amp DNO supply Background, So I have an 18th Ed compliant consumer...
Replies
9
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock