Discuss Separate Arc fault protection devices not needed with RCD's? in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
1
I'm looking at replacing my old switchboard with a new RCD/AFCI one. I asked the electrician who was quoting the job about Arc fault interrupters. I previously understood these were a different device from RCD's-RCD is to prevent shocks, AFI to prevent fires.
I also understood there were devices that did both in combination.

The electrician tells me that the tech has advanced so that RCD's alone will be sufficient without incorporating the AFI feature. If a switch contact or wire etc wears out and arcing occurs, the newer RCD's I'm told will still trip and cut off the power to that circuit, preventing a fire. Is that correct? He seemed pretty adamant about it. I do want to minimise the risk of electrical fires, so just wanted to see what others thought.

Thanks
 
The devices work in different ways.

An rcd looks for an imbalance between the load of line and neutral on the protected circuit… if the imbalance goes over a threshold, it trips out. Imbalance is caused by leakage to earth.

arc fault can happen where there is no contact with earth. A loose connection where the cable is touching where it’s supposed to be, but is loose and may disconnect momenterily. This causes the arcing, and very high temperatures, which in turn can cause a fire
 
When does it get bad enough to causing the leakage and arcing, will the RCD cut the power soon enough to prevent a fire from getting going?
In many cases yes. Where the fault is weakening insulation between line and earth somewhere (which is commonly the case for damaged cables due to crusing or rodent attacks) the GFCI (USA name) / RCD (UK/EU name) will see the current going astray and disconnect. This is sometimes called a "parallel arc" as it is between adjacent conductors.

The usual over-current protection does the same eventually, but it can take a lot more current to do so (tens of amps or more, versus 0.03A or so) and that implies a lot more local heating and so a higher fire risk than an RCD in the same circumstances.

The AFCI (USA name) / AFDD (UK/EU name) operates differently as it is looking for the high frequency noise from an electric arc, not for unusual conventional current flow, and so it can also detect a break in a conductor leasing to a "series arc" where the normal current is flowing but now having to jump a small gap to continue. That gap suffers from a lot of heating as a result and so is also a fire risk. Really this is the special protection from an AFDD that is not provided by more traditional means.

Now quite how good or useful this protection is in practice, and how many fires are really a result of arcs that only an AFDD would detect, is open to debate!

Fires can start from other faults like a high resistance connection (local heating but no arc) or bad design/workmanship (too small a cable for the over current protection), failing parts like motor run capacitors inside appliances, or even common ones like lint in tumble dryers catching fire and being classed as "electrical fires" at source. None of the suppliers of AFDD or the standards bodies have given such an analysis to my knowledge, so the cost/benefit is unknown.

TL;DR Combined RCBO/AFDD devices that provide all of the protection modes are safer, but to an unspecified amount, cost more, and may have more nuisance trip events where no fault is found.
 
I got a second opinion from another firm. They are willing to provide the combo AFCI/RCD devices but they don't think the arc protection is necessary. This is because the wiring is tough plastic sheathed cable and the visible wires behind the board look good he said. The house is 40 years old, but I'm also going to have the old wall outlets and light switches replaced which by itself should reduce the chances of arcing anyway right?

They say because the combo AFCI/RCD devices are bigger the new board would take up a lot more space than the current one and I might end up having to get a plasterer or builder to patch up part of the wall. Hmm

I also never have any issues with fuses/breakers tripping, no sparks, burn marks, bad smells or buzzing sounds, so with all that in mind, is it worth getting the arc protection or would the standalone RCD's be sufficient?
 
The number of dangerous situations prevented by a RCD in an installation will outnumber the amount of dangerous situations prevented by an AFCI by several orders of magnitude, so if the choice was one or the other, the RCD wins out every time.
That doesn't eliminate the rare event when a AFCI does save the situation, of course.
 
The number of dangerous situations prevented by a RCD in an installation will outnumber the amount of dangerous situations prevented by an AFCI by several orders of magnitude, so if the choice was one or the other, the RCD wins out every time.
That doesn't eliminate the rare event when a AFCI does save the situation, of course.

The RCD

Electricians best friend after the Voltstick

I've got more handy money from RCD trips than anything else

Can't depend on either of them but wouldn't be without them
 

Reply to Separate Arc fault protection devices not needed with RCD's? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

These are going to become the norm aren't they? I've been reading this...
Replies
10
Views
2K
Hi there , Currently doing a college project where i need to select protective devices for the contract. I'm now at the point of selecting SPDs...
Replies
5
Views
2K
I'm planning a replacement for my existing domestic CU and would like to have it sanity checked before I get an electrician involved. The main...
Replies
33
Views
4K
Page 337 cites UL testing, where arc resistance was found to be only 30 milliohms...
Replies
0
Views
749
Hi all, The rcd in my single rcd consumer unit keeps on tripping. It first happened when I turned the kettle on. It then happened when I turned my...
Replies
7
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock