However when I re-energised the circuit and plugged the appliances back in there was a crack, a small bang, and a weird (perhaps acidy) smell, which I understand to be a short circuit.

No, that is not a short circuit, that is two noises and a smell, these could have been caused by a short circuit or an earth fault.

A short circuit is a connection of negligible resistance between live conductors, an earth fault is a connection of negligible resistance between one or more love conductors and earth.
 
0.43 could be caused by an RCD socket or spur. It could also be a filtered extension lead (have you tested at 250v?).
Testing an existing circuit you should have your neutral conductors disconnected and linked to the line conductors, keep the cpcs connected. Do not test line to neutral unless everything is disconnected.
 
0.43 could be caused by an RCD socket or spur. It could also be a filtered extension lead (have you tested at 250v?).
Testing an existing circuit you should have your neutral conductors disconnected and linked to the line conductors, keep the cpcs connected. Do not test line to neutral unless everything is disconnected.
Thanks Westward.

So how I've been taught to perform an IR test:

  • CB safely isolated
  • MFT in Isolation mode at 500v
  • Zero by touching probes together
  • Test N/E, L/E, L/N
  • Probes at at top of breaker (for line) or terminals at top of board (for N & E)
 
That is fine for a new initial verification but this is an existing in use circuit. Your zero across L and N was probably something still connected across the circuit. Test as suggested in #13.
 
0.43 could be caused by an RCD socket or spur. It could also be a filtered extension lead (have you tested at 250v?).
Testing an existing circuit you should have your neutral conductors disconnected and linked to the line conductors, keep the cpcs connected. Do not test line to neutral unless everything is disconnected.
Hi Westard. I've been back to this installation again.

Re "Testing an existing circuit you should have your neutral conductors disconnected and linked to the line conductors, keep the cpcs connected" - do you mean that at the board I leave the CPC connected and remove the line and neutral conductors for the relevant circuit and connect them with a jump lead? So as per the attached illustration?

Once I'm clear on that and I'm back at the installation I'll perform the test, but in the meantime I corrected a couple of mistakes I realised I had made with the wiring and retested as per post 14 and have different (better?) results:

Neutral to earth: >999
Line to earth: 0.31
Line to neutral: >999

As I understand it my Line to Earth is my issue as less than 2 mega ohms is a fail.

I've been around the ring circuit unplugging everything and identified a few accessories that I hadn't previously been aware of: a spurred electric radiator, its switch (which has a couple of neons), a socket with a USB port. I disconnected all these and - to maintain the ring - joined the relevant conductors (earth to earth, line to line, neutral to neutral) together with jump leads / wagos (which I presume was the correct thing to do???).

This made no difference however, the reading remained at 0.31.

One theory: 4 of the double sockets have tiny neon on/off lights on the switches - could that be responsible for the reading? Or am I simply overlooking something that's still in the circuit?
 

Attachments

  • Screenshot 2024-03-26 at 17.20.20.png
    596.1 KB · Views: 8
I disconnected all these and - to maintain the ring - joined the relevant conductors (earth to earth, line to line, neutral to neutral) together with jump leads / wagos (which I presume was the correct thing to do???).
If you've broken the ring up, leave it broken and test the individual sections.
 
Hi Westard. I've been back to this installation again.

Re "Testing an existing circuit you should have your neutral conductors disconnected and linked to the line conductors, keep the cpcs connected" - do you mean that at the board I leave the CPC connected and remove the line and neutral conductors for the relevant circuit and connect them with a jump lead? So as per the attached illustration?

Once I'm clear on that and I'm back at the installation I'll perform the test, but in the meantime I corrected a couple of mistakes I realised I had made with the wiring and retested as per post 14 and have different (better?) results:

Neutral to earth: >999
Line to earth: 0.31
Line to neutral: >999

As I understand it my Line to Earth is my issue as less than 2 mega ohms is a fail.

I've been around the ring circuit unplugging everything and identified a few accessories that I hadn't previously been aware of: a spurred electric radiator, its switch (which has a couple of neons), a socket with a USB port. I disconnected all these and - to maintain the ring - joined the relevant conductors (earth to earth, line to line, neutral to neutral) together with jump leads / wagos (which I presume was the correct thing to do???).

This made no difference however, the reading remained at 0.31.

One theory: 4 of the double sockets have tiny neon on/off lights on the switches - could that be responsible for the reading? Or am I simply overlooking something that's still in the circuit?
Bumping this up
 

Reply to Short in socket - why/how? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Grateful if someone could offer some advise, I'm struggling to find a definitive answer to this. I have a double socket, it was on the ring main...
Replies
8
Views
743
We have a room in the house that was the kitchen. That has been relocated to a different area, so the old kitchen has been sold off and the room...
Replies
2
Views
669
I'll start by saying - I have absolutely no intention of doing any wiring or anything electrical myself. You get someone professional to do a...
Replies
8
Views
903
Hey, I lifted a few sockets from a wall so I could paint without having to cut in around them. I haven’t lifted any light switches yet. When...
Replies
4
Views
950
Hi everyone. Hopefully someone can help with a little mystery i had today. The issue is fixed but I want to understand what was going on to help...
Replies
8
Views
688

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock