Thanks showerq for the brilliant detailed reply. From everything I've read I suspect it's down the the supply companies, but I could be wrong. It's difficult to diagnose from afar. I really wish you all the luck.

I am a I little concerned you didn't get any certification.

Cheers peter
 
Hi - the company may have their Electrical registration listed on their website or paperwork. If you're interested someone here may be nearby and be able to have a look at the issue close up.

Hi Wilko,

I've contacted NICEIC and ELECSA (who I was told are the same company from the man I spoke to at their technical dept.) and also ECA. They have all said contact the electric board as it sounds like a supply issue. Hopefully now they have agreed to send someone out again they can let us know. If all is fine (and I hope so) then I don't know what our next step is.
 
Did the shower installer walk away without operating the shower? The lights must have been flickering straight away. That should have told the installer something was a miss.
It may be that they have installed something larger than was there before, but that would dim the lights, not cause a flicker.

The shower pull cord is linked to a fan? For extraction? These are normally wired in with the lighswitch rather than the shower.

If you can, please post a photograph of your shower and your consumer unit/meter/etc. (ps, the service head is where the supply cable goes through a big fuse, and normally is sealed so us mortals cannot tamper)

We don't want to badmouth any company on the public forum, so don't name them.
 
Thanks showerq for the brilliant detailed reply. From everything I've read I suspect it's down the the supply companies, but I could be wrong. It's difficult to diagnose from afar. I really wish you all the luck.

I am a I little concerned you didn't get any certification.

Cheers peter

Many thanks again, Peter.

I shall ask they shower company for the certificate. Fingers crossed and again many thanks to you all.
 
Did the shower installer walk away without operating the shower? The lights must have been flickering straight away. That should have told the installer something was a miss.
It may be that they have installed something larger than was there before, but that would dim the lights, not cause a flicker.

The shower pull cord is linked to a fan? For extraction? These are normally wired in with the lighswitch rather than the shower.

If you can, please post a photograph of your shower and your consumer unit/meter/etc. (ps, the service head is where the supply cable goes through a big fuse, and normally is sealed so us mortals cannot tamper)

We don't want to badmouth any company on the public forum, so don't name them.
Flicker and Dim may mean the same to some Mate, before we start why not wait until the OP comes back with answers to the questions posed, I've seen dafter things than what I am questioning, and of course we are all diagnosing the problem from afar.
 
Did the shower installer walk away without operating the shower? The lights must have been flickering straight away. That should have told the installer something was a miss.
It may be that they have installed something larger than was there before, but that would dim the lights, not cause a flicker.

The shower pull cord is linked to a fan? For extraction? These are normally wired in with the lighswitch rather than the shower.

If you can, please post a photograph of your shower and your consumer unit/meter/etc. (ps, the service head is where the supply cable goes through a big fuse, and normally is sealed so us mortals cannot tamper)

We don't want to badmouth any company on the public forum, so don't name them.

Hi Littlespark, Thanks for your reply.

They tested the shower before they left, however, the flickering only started in the evening on the day it was installed.

I recorded the whistle and played it as it didn't happen when they were here. A few hours later after they replaced the washers, solenoid and ball valve the same whistle happen again and is continuing when the shower is on as is the lights flickering. We are waiting for them to come out and look at it again.

Thank you about the pull cord - we shall double check as no one has mentioned or suggested that before. Thank you.
 
@littlespark. ain't you ever heard of the seal fairy? :D:D:D.

(ps, the service head is where the supply cable goes through a big fuse, and normally is sealed so us mortals cannot tamper)
 
alaerm bells ringing. why is a fan running off the shower circuit, unless it had been designed as such by manufacturers?

O dear. I've seen this before. Extractor permanent live and neutral fed from lighting circuit. Switched live from shower.
It functionally worked fine at the address I was at but obviously wrong.

This property was previously owned by a builder. He had done a lot of interesting things including the shower run off 2.5 mm. I've no idea how it coped, but the cable was fine, no evidence of overheating. This turned into a full rewire of the whole house as the socket circuits and lighting were a joke too. First time I've made a customer cry when going over what I'd found.
 

Reply to Shower on Ceiling Light Flickers - advice needed please in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I am not an electrician but am looking for some advice as to how to fix my sporadic light flickering problem that has come and gone for the year...
Replies
24
Views
2K
I have 16 ceiling spots to be replaced in a room being repurposed as a bathroom. Some will be over a shower, basin and bath hence need to be IP65...
Replies
19
Views
1K
Hello all- I hope this is the right place to ask this question. A few weeks ago the LED lights in the kitchen started flickering intermittently...
Replies
2
Views
725
Hi all. Sort of an interesting one. I had a call from a client to say she is getting a shock when using the shower. I told her not to use it and...
Replies
15
Views
2K
Hi I'm in need of some advice. First of all i'm not an electrician but do have an understanding of electrics as i come from an electronics...
Replies
4
Views
656

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock