I've been asked to wire a shed the customer said that he has got the cable when I looked at the cable it was single core like pme cable I guess the neutral and earth are both in the armoured sheath has anyone used this cable before?
 
It could be concentric or split concentric. Neither can be directly buried. Concentric you can’t use at all for domestic systems.

If you don’t know what I’m talking about, find an electrician that does.
 
Click HERE

splitconsentric2.jpg
 
Last edited by a moderator:
split con has seperate insulated neutral cores for tn-s
con just has bare outer cores for tn-c-s.

as both types still require rcd protection , they have rather limited use for sub-mains or exterior circuits.
 
There is a large electrical contracting company in my area that uses split concentric cable for sub - main cable between the DNO's OMB and consumer units when distance is more than 3 mtrs. They have been doing it for years. Easier to install than SWA cable.
 
There is a large electrical contracting company in my area that uses split concentric cable for sub - main cable between the DNO's OMB and consumer units when distance is more than 3 mtrs. They have been doing it for years. Easier to install than SWA cable.

Are the DNO happy with this? I only ask as EDF specify 25mm SWA?
 
Id consider its use in dedicated risers for flats, tied to tray. Risers in flats are very rarely disturbed, so there's almost no chance of damage.
There's not many other places I'd use split con.
 
johnboy6083;787181[COLOR=#ff0000 said:
]Id consider its use in dedicated risers for flats,[/COLOR] tied to tray. Risers in flats are very rarely disturbed, so there's almost no chance of damage.
There's not many other places I'd use split con.
probably caus thats where its often used.....
 
split con has seperate insulated neutral cores for tn-s
con just has bare outer cores for tn-c-s.

as both types still require rcd protection , they have rather limited use for sub-mains or exterior circuits.

Biff. plain concentric can NOT be used after the DNO cutout!Under any circumstances!

Split concentric on the other hand can be when the proper regard to protection is observed.
 
Biff. plain concentric can NOT be used after the DNO cutout!Under any circumstances!

Split concentric on the other hand can be when the proper regard to protection is observed.
well i would`v thought this was common sense Tony as well....
i mean is TN-C allowed in the UK for consumer install?....er..NO!!
 
I've been asked to wire a shed the customer said that he has got the cable when I looked at the cable it was single core like pme cable I guess the neutral and earth are both in the armoured sheath has anyone used this cable before?

There is no armouring on this cable, the concentric wires are the actual neutral and earth conductors. This cable is fine for the DNO's as the terminations and spreading of the conductors are hidden within the cut-out. It's a different matter for termination into standard electrical components (CU's/DB's and the like), and unless you know what your doing, can very easily end up looking like an amateurish pigs ear of a job!! The best and easiest solution is using a 3 leg heat shrink breakout and heat shrink tubing for the gathered concentric conductors.

The only way i would ever use this type of cable for underground installations, is within a heavy duty (thick walled) PVC duct, buried at a suitable depth. Which by the sounds of it, is what your going to have to do, if your going to use the customers cable!! Never install this type of cable in a direct buried situation.... Apart from anything else, it won't conform to the requirements BS7671...
 
There is no armouring on this cable, the concentric wires are the actual neutral and earth conductors. This cable is fine for the DNO's as the terminations and spreading of the conductors are hidden within the cut-out. It's a different matter for termination into standard electrical components (CU's/DB's and the like), and unless you know what your doing, can very easily end up looking like an amateurish pigs ear of a job!! The best and easiest solution is using a 3 leg heat shrink breakout and heat shrink tubing for the gathered concentric conductors.

The only way i would ever use this type of cable for underground installations, is within a heavy duty (thick walled) PVC duct, buried at a suitable depth. Which by the sounds of it, is what your going to have to do, if your going to use the customers cable!! Never install this type of cable in a direct buried situation.... Apart from anything else, it won't conform to the requirements BS7671...
and i`v heard of this going on in the past eng....this type of cable buried direct....
as I have already pointed out its commonly used in ducted risers (for flats and the like) ...but i`v heard of it being substituted for SWA....in a completely impractial and non-compliant fashion...
 
The outer serving on DNO concentric cable is a tough as old boots. It will take a lot more that a spade to break through it.

I acquired some to have a experiment with.
 
quote_icon.png
Originally Posted by driverman
There is a large electrical contracting company in my area that uses split concentric cable for sub - main cable between the DNO's OMB and consumer units when distance is more than 3 mtrs. They have been doing it for years. Easier to install than SWA cable.



Are the DNO happy with this? I only ask as EDF specify 25mm SWA?

Yes.......I worked for EON @ the time now WPD. I was surprised myself but all Ok with the DNO.

Sorry, that was my reply to a question by Phoenix
 

Reply to single core in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

A friend of mine got a 2nd hand coffee machine (OK, probably 3rd or 4th...) for use in a charity cafe and it has problems. First problem is no...
Replies
1
Views
158
A friend of mine wired a 10mm 3 core armoured cable to his shed before I got involved and wired it himself already. He wants make it an air bnb...
Replies
8
Views
927
I have a scenario where there is a three phase DB in a commercial property where there are mixture of three phase and single phase washing...
Replies
2
Views
877
Hi I have inherited a compressor with a single phase motor but its been stripped and I need to fathom out what's what.. I don't know if it even...
Replies
13
Views
657
Hi guys, I don’t really know where to post this, sorry if it’s in the wrong place. After posting a thread about old lead sheathed cable in my...
Replies
22
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock