you have a 40Kw generator in a vast expanse of concrete genny is also raised up on 6x6 wood timbers
one earth electrode
genny works fine all voltages check etc
you should be able to test the electrode with the bloody earth loop tester but that doesn't work.
to confirm its a three wire tester one one live one on neutral one on the earth thats only connected to earth.
how else would you confirm the earth
stakes can't be used concrete
stakeless can't be used no parallel path
 
Last edited by a moderator:
Thanks but unfortunately no the neutral and earth are linked together. It did confirm things i already knew.

something is not right i'm just not seeing it.
 
The only way you can measure the resistance of the earth electrode in this situation is with a proprietary earth electrode tester as the earth electrode is not used as the means of earthing, only to reference the genny the the general mass of earth.
 
But how do you do that if you can't use a staked method tester because of the concrete there is some pipes maybe but their no where near in a straight line.
And clamped meters won't work because there is no parallel paths
 
Ships,

Is this a temporary generator installation, or is it going to be permanent source of power to an installation, be it stand-by or prime power??
 
But how do you do that if you can't use a staked method tester because of the concrete there is some pipes maybe but their no where near in a straight line.

Did you install the electrode by drilling down through this concrete then, or did you run the coductor to more suitable ground???


Are there any extraneous or exposed conductive parts from any other electrical systems in close proximity to the genny at all??
 
Its a girder going down into the ground other girders are nearby but connected together so you'd just measure the resistence of the girders not its suitability to earth.
In real terms it should be an amazing earth and very suitable but i would like to perform a test and confirm it so you can see it in black and white.
 
could you use an earth electrode tester, and ensure your test rods are a long distance from the steels, in order to get an accurate reading. Say you place your test rod at 60m away and your reference rod 100m. That would give you a reading, and tell you if it is suitable. I'm happy to hear other suggestions?
 
Last edited:

Reply to Single earth electrode generator in the Australia area at ElectriciansForums.net

Similar Threads

I realise this overlaps with the Earth Rod install post a little, but I am attempting to plan part one of an upgrade. Currently I am mostly...
Replies
24
Views
6K
Having a bit of a nightmare with what should have been a simple job. Back in January I replaced some old Varilight dimmers which had failed after...
Replies
6
Views
1K
Hi new here so take it easy chaps !! A client of mine wishes to supply their catering van from a new generator they are purchasing, I believe it...
Replies
14
Views
8K
I need to clarify something that's rattling around in my head. I was taught when testing lightning protection systems that the maximum...
Replies
11
Views
3K
Hi I am a sparks from the 15th Ed, did 16, 17 and last year 18th. I am out of practice though as have been office based for 12+ years in a...
Replies
8
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock