Hi guys,

Been given a motor and associated control gear within a panel that has been water damaged.

This motor has 3 windings U1/U2, V1/V2 and Z1/Z2, 1 pair of wires for the brake and 1 for cut-out I believe.

In the process of wiring a new panel up for it and it know its a long shot but can anyone provide a diagram for wiring a single phase motor with centrifugal switch that also is reversing.

I believe Z1/Z2 switch polarity to make this happen.

Cheers
 
With those terminal markings I would normally expect:
U1 / U2 = main winding
V1 / V2 = centrifugal switch
Z1 / Z2 = auxiliary winding (capacitor winding if cap(s) fitted.)

Yes, to reverse direction, the auxiliary winding is reversed relative to the main. You can do it with two 4-pole contactors or three 2-pole (line, forward, reverse). Forward and reverse should be interlocked electrically and/or mechanically. Depending on application and whether the motor is PSC, cap start or cap start and run, the control circuit might need to be interlocked with the centrifugal switch, to prevent the motor re-starting in the same direction if an attempt is made to reverse it while still coasting above switch operating speed. Again according to application this might have significant safety ramifications and proper RA and design is necessary.
 
With those terminal markings I would normally expect:
U1 / U2 = main winding
V1 / V2 = centrifugal switch
Z1 / Z2 = auxiliary winding (capacitor winding if cap(s) fitted.)

Yes, to reverse direction, the auxiliary winding is reversed relative to the main. You can do it with two 4-pole contactors or three 2-pole (line, forward, reverse). Forward and reverse should be interlocked electrically and/or mechanically. Depending on application and whether the motor is PSC, cap start or cap start and run, the control circuit might need to be interlocked with the centrifugal switch, to prevent the motor re-starting in the same direction if an attempt is made to reverse it while still coasting above switch operating speed. Again according to application this might have significant safety ramifications and proper RA and design is necessary.
Thanks for your reply, its much appreciated.

The new contactors are mechanically interlocked and the brake is wired through the N/O auxiliary contact of both contactors in parallel.
 

Reply to Single phase motor reversing with brake and centrifugal switch in the Electricians' Talk area at ElectriciansForums.net

Similar Threads

I posted a month ago regarding a single phase motor + panel I have been given to try and sort following water damage to the panel. The assembly...
Replies
0
Views
1K
Hi I have inherited a compressor with a single phase motor but its been stripped and I need to fathom out what's what.. I don't know if it even...
Replies
13
Views
639
I previously posted about having a single phase reversing motor which I thought had a centrifugal switch. After looking into it more, it actually...
Replies
1
Views
1K
Hi, As a DIYer I`ve quite a bit of wiring up domestic house single phase experience but no 3 phase experience. So I have been offered a two post...
Replies
7
Views
2K
evening all ive got a single phase AC fan motor running normally however occasionally on start up it starts in reverse. i have 4 no fans, and this...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock