Discuss Sky high ze reading in the UK Electrical Forum area at ElectriciansForums.net

On an EICR that would be a C2.

I guess they are applying the same rules as us, C2 requires urgent remedial action but you would not normally be expected to disconnect the installation because of it.

That is of course on the basis that they plan to do something about it.
 
Hello fellas. Had the dno trying to tell me that a 19 ohm ze reading on a tns system was ok to leave energised? Seriously? Can someone please explain to me how that is ok
TN-CS (PME) 0.35ohms TNS - 0.8ohms did they come round to test it or was it over the phone you told them .so a higher ZE may not be an issue if the dno decide that its down to network parameters. All they would do is ensure the main fuse is sized appropriately.
 
Did you speak to anyone of importance on the phone or just the trained chimp who answered the phone?
 
Hello fellas. Had the dno trying to tell me that a 19 ohm ze reading on a tns system was ok to leave energised? Seriously? Can someone please explain to me how that is ok?

only the person who told you it is ok can tell you why they said that, we cant read their minds any more than you can.

Exactly what did they say about it? did they say it is ok for now until we can get it fixed or that it is ok permanently? did they confirm whether the installation had suiatble RCD protection to make this ok as a short term soloution?
 
Hello again. It wasn’t me who spoke to them on the phone so I have no idea if they were important. I installed a new fuseboard and when it came to testing the ze i obviously came across the reading. They sent someone out and that was when he told me the reading is fine providing it has suitable rcd protection, which it has. It’s a full rcbo board and the operating times were well within boundaries. I didn’t argue with him as I don’t deal with their side of things and therefore wouldn’t question that I know more about his job than him but personally I would not have been happy to walk away and leave it. They are supposed to be going back tomorrow morning to fix the issue though
 
So they haven’t ignored it then? As it has suitable RCD protection then they deemed it safe for continued use until they can rectify the poor earthing fault.
 

Reply to Sky high ze reading in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

On an EICR I found a 200 amp 3ph supply, TNS earthing (which looks original) and Ze of 19 ohms. No rods. No RCDs. L1 -> N was about 0.5 ohms...
Replies
11
Views
1K
Hello there. I've been looking around here and found some conflicting information. I have a question if I may ask. I had an electrician come over...
Replies
30
Views
4K
High Ze on a tns supply. It’s 1.48 ohms. Weird as I did a Ze here 4 weeks ago and it was 0.50. Do DNO come out for a Ze that high what is likely...
Replies
23
Views
4K
Fluke MultiFunction Tester 1662 TNS Earthing system. Switchboard - 415v - 3 Phase + Neutral + Earth. MCB 1000A 3 individual Earths (185mm)...
Replies
22
Views
3K
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock